Heat Pump Icing
Awesome Bill!
The temperature of the return air right at the evaporator coil is 100 degrees.
Here's my point...
When you are calculating the delta-t across the evaporator coil, you need to take the delta-t ACROSS THE EVAPORATOR COIL, NOT THE WHOLE AIR DISTRIBUTION SYSTEM!
Taking readings at return or supply grills may be convenient, but they are not as useful as temperature readings taken right before and right after the cooling coil.
The system that I presented to you was working perfectly as far as the refrigeration circuit was concerned. That was, of course, until we added tons of refrigerant to the system.
The only problem with the system was that the flexible return duct had separated from the collar on the return plenum.
The 80 degreee supply air was perfect given the 100 degree attic (return) air temperature.
Awesome job, guys!
Until the next one.
  • Eugene Silberstein 3
    Eugene Silberstein 3 Member Posts: 1,380
    What do you think?
    Sorry about the topic of HEAT PUMP ICING. This post is not about heat pumps, nor icing coils.
    You are on a no-cooling call. The system is a straight-cooling unit with a fixed bore metering device. The air handler is in the attic and the condensing unit is in the back yard.
    You take a reading at the return grill in the bedroom hallway and the temperature is 85 degrees. You take a temperature reading at a supply register and you find the temperature of the supply air is 80 degrees.
    You calculate the 5-degree delta-t across the evaporator coil and surmise that the refrigerant charge is low. To be sure, you measure the condenser subccoling and the evaporator superheat. The evaporator superheat is 15 degrees and the condenser subcooling is 20 degrees.
    You decide that the system is short of refrigerant, so you go to the truck and get your tank of R-22. You add refrigerant to the system. The superheat drops to 3 degrees and the condenser subcooling rises to 35 degrees. The temperature of the supply air is now 79 degrees, while the return air temperature remains at 85 degrees.
    Since the supply air is cooling a little better (1 degree cooler), you decide to add more refrigerant. The evaporator superheat is now zero degrees and the condenser subcooling is now 45 degrees. The temperature of the supply air remains constant at 79 degrees and the return air remains constant at 85 degrees.
    Considering the information provided, what do you think is the most likely cause for the system malfunction? What would you do if you were the follow-up technician?
  • don_156
    don_156 Member Posts: 87
    I would
    go get my recovery bottle and start recovering all that freon I just put in the unit.
    Then before I get started I would first check the fan motor
    to see if its working properly,then I would check the ductwork...then I would properly ask the customer why the filter has not been change,and then if I still can not figure why their no load on the coil,I would pick up the phone and call the professor.
  • Jeff Lawrence_24
    Jeff Lawrence_24 Member Posts: 593
    Don's right
    I'd look at the fan and see if it's running and then check the evap coil....
    Definitely
    The system is definitely overcharged now.... It wasn't before.
    Let's assume that the blower in the air handler is operating fine.
    What would you check on the ductwork, Don? You are definitely getting warm.
    Let's say the blower is operating and the coil is clean....
    If the filter was dirty, the delta-t across the evaporator coil would be high. The same holds true for a defective blower or a dirty evaporator coil.
    Hmmmmmmmmmmmmmmmmmmmmmmm... Quack quack
  • don_156
    I would
    > wasn't before.
    > What
  • don_156
    I would
    first check my delta t at the airhandler and see if the reason for the low delta t was because of lack of insulation on my ducts or air leaks.
    However if I may say that sometime low delta t could be from the blower speed being set to high as well.
  • thp_7
    thp_7 Member Posts: 20
    Big air
    To much fan speed!
  • thp_7
    Big air
    Sounds like your average 2ton a-c installed on a 100,000btu 90%. In short to much air flow across the A coil.
  • don_156
    You have
    > the A coil.
    MMMMaybe
    But, too much airflow across the coil would still result in a lower supply temperature...
    Very good try and thanks for playing.
  • thp_7
    Whats your suction #
  • don_156
    You have
    to watch the Professor when he ask his question thp,he can
    be very tricky.
    But thats a good thing!
    After...
    After adding all of that refrigerant, our suction pressure is absolutely through the roof, so you better have your DOT approved recovery tank handy!
    soooooooooo.... what are we looking for in the duct system?
  • bill_61
    bill_61 Member Posts: 5
    return temp where???
    you said you took your return temp from the hallway return grille??? whats the return temp in the ductwork right at the air handler, punch a hole in the ductwork and take it, i doubt you would even have to remove much insulation because there probably isn't any and the attic is a sweltering 120 degrees making the return temp close to 100 degrees...that would be a good delta t if your supply air is 80
  • thp_7
    The easy way to spot this
    would have been seeing that you would have had to had a suction pressure in the 100# range with all other things normal.