orifice rick,the oriface is sized according to the capacity of the compressor.in a lot of cases the only diff
between a 2 and a 2.5 ton will be the size of the oriface.
this will make a differance maintaining control over the refrigerant or flooding back.a fixed oriface is a comprimise situation to begin with.so change to the recommended oriface
mike terry
mike terry
orfices
Installed furnace with package coil .Sized house .ac load is 2 tons. I received a package coil that is 2.5 tons .wholesaler says thAT IS FINE CHANGE ORFICE THAT COMES WITH CONDENSING UNIT. SHOULD I KEEP[ ORFICE FOR 2,5 TONS OR SWITCH ORFICE.TO MATCH UNIT.0 -
sorry rick
I cant seem to spell orifice.0 -
Change That Orifice
Sounds like the name of a new game show....
As mentioned, the orifice should match the capacity of the compressor/condensing unit.
To make life easier in the future, mark the side of the furnace/air handler with the number of the orifice that is installed as well as the date on which the orifice was installed/replaced/checked.
THANKS .I SEEM TO FIXING AND INSTALLING EVERYBODYS AC EXCEPT MINE .WILL GET THE CORRECT ORFICE AND FINISH THE INSTALL AFTER THE HEAT WAVE.0