Color coding
Dale
Dale Member Posts: 1,317
Since this is a safety sensitive job go with the colors and ID tape and make sure there are plenty of valves in accessible spaces. I looked at a gas system in a local high school where the gas valve for the chem labs was behind a locked door.
  • Mike Lundstrom
    Mike Lundstrom Member Posts: 10
    I was just wondering if anyone knew if there was an industry standard for piping colors in a building ( an ASHRAE standard perhaps). We (school division) are construcing a new building and are looking for a standardized color system. We have hot water, chilled water, glycol, domestic hot, domestic recirc, kitchen hot water, kitchen recirc, and natural gas. Any direction or suggestions are always appreciated.
    Mike L.
  • Michal
    Michal Member Posts: 213
    here is a good source for you
    here is a good reference for you, hope it helps
    Colors: Provide paint colors shown on contract drawings or to be selected by the Director from finish paint manufacturers available color selections.
    1. Approved finish paint manufacturers to match designated colors of other manufacturers where colors are shown on contract documents.
    2. Color Coding: Apply exposed insulated and uninsulated piping finish paints in the following colors when piping is located in the following applicable rooms or spaces:
    a. Applicable Rooms and Spaces: Mechanical Equipment Rooms, Steam Service Rooms, Refrigeration Machine Rooms, Boiler Rooms, Penthouse Mechanical Equipment Rooms and Power Houses.
    b. Existing Facility Buildings: Color code to match Facility’s color code.
    c. New Facility Buildings: Color code as follows:
    1) Air, Compressed: Safety Green.
    2) Air, Control: Safety Green.
    3) Air, Medical: Safety yellow.
    4) Ammonia, Gas and Liquid: Safety Yellow.
    5) Brine: Safety Green.
    6) Carbon Dioxide: Safety Red.
    7) Dangerous Materials: Safety Yellow.
    8) Engine Exhausts: Safety Yellow.
    9) Fire Protection Systems; Fire Standpipe, Sprinkler, and Wet Chemical Systems: Safety Red.
    10) Flue Gases: Safety Yellow.
    11) Gas, Natural and Manufactured: Safety Yellow.
    12) Gasoline: Safety Yellow.
    13) Glycol and Glycol/Water Mixtures: Safety Yellow.
    14) Nitrous Oxide: Safety Blue.
    15) Oils, Fuel and Lubrications: Safety Yellow.
    16) Oxygen: Safety Green.
    17) Pneumatic Tube System s: Safety Green.
    18) Refrigerants: Safety Yellow.
    19) Sewers, Storm and Sanitary: Safety Yellow.
    20) Steam; Supply, Condensate Return and Exhaust: Safety Yellow.
    21) Vacuum: Safety Green.
    22) Vent, Atmospheric: Safety Green.
    23) Water, Up to 140 Degrees Fahrenheit: Safety Green.
    24) Water, 141 Degrees and Above: Safety Yellow.
    d. Other Colors:
    1) Exposed Ductwork: Gray.
    2) Insulated and Uninsulated Equipment: Gray.
    a) Do not paint equipment with factory finish paint.
  • Mike T., Swampeast MO
    Mike T., Swampeast MO Member Posts: 6,928
    Covered under ANSI A13.1
    Here are some common conventions based on that standard:
    Fire Protection Riser or Unexposed Fire Protection Piping — Red
    Steam Supply — Orange
    Condensate Return — Aluminum
    Potable Cold Water — Dark Green
    Potable Hot Water — Dark Yellow (Gold)
    Non-Potable Water — Bright Yellow
    Lab Cold Water — Light Green
    Lab Hot Water — Light Yellow
    Chilled Water — Dark Blue
    Condenser Water — Light Grey
    Natural Gas — Light Yellow
    Compressed Air — Dark Brown
    Vacuum — Beige
  • BillW@honeywell
    BillW@honeywell Member Posts: 1,099
    Save some money...
    Thomas & Betts/Westline used to make a whole series of industrial quality "Snap Around" or ty-wrap fasten or adhesive signs, arrows and labels that were very easy to install, properly color coded and looked really nice in a boiler room or mechanical room. They were sold thru safety equipment distributors. I'm not sure if TB/Westline is still in business but I'm sure this stuff is still available, just try an industrial safety equipment company in your area.
  • Mike Lundstrom
    Thanks for your guys' help.
  • Firedragon_4
    Firedragon_4 Member Posts: 1,434
    Check this out too!
    > Mike L.
  • Firedragon_4