Primary-Secondary question
Options
Scott Denny
Member Posts: 124
Running a primary-secondary setup off a Munchkin to two fan coils. Since one fan coil is in a remote location, should I run the primary loop out to it or can one secondary loop be substancially longer than the other?
0
Comments
-
A secondary loop
can be as long as you need it to be, as long as you size it, and its circulator, correctly.Retired and loving it.0