sizing a water heater
Tom_53
Tom_53 Member Posts: 43
I have a customer that just installed a 70 gallon tub. They are running out of hot water. They have a 30 gallon oil fired heater. Iam considering a 50 gallon bock and a f5 riello. There boiler is a Utica Starfire 111, 4 section, & f5 riello. When the boiler was installed it included a switching relay with priority, for the possible future indirect. I am not sure what to recomend, what do you think?
Thanks in advance,Tom
  • Alan R. Mercurio_3
    Alan R. Mercurio_3 Member Posts: 1,624
    Ok first you need to measure the doorway the water heater is going through.. :)~ I'm just kidding here's a helpful link for you.
    Your friend in the industry,
    Alan R. Mercurio
    www.oiltechtalk.com
  • Tom_53
    To Alan
    Hi Alan, Thanks for the response. I can not get on your web site. I tried a new password, I GAVE UP! I miss your old format on OTT.
    Thanks again,
    From Tom
    Tom, You're very welcome and I apologize for the difficulty you're having getting on the web site. If you would like e-mail your phone number to me and I will contact you tomorrow so I can help you get back on the site with our fellow technicians.
    Alan R. Mercurio
    www.oiltechtalk.com
  • Dave Yates (PAH)
    Dave Yates (PAH) Member Posts: 2,162
    calcs
    Take your bathing temp (let's say that's 106 F) minus the incoming temp (say 40 F in winter) divided by the storage temp (120 F?) minus the inlet temp (40 again). That's the percentage of flow that represents the hot water injected into the mix.
    Turn on the shower; adjust to suitable temp; time the fill for a 2-gallon bucket; and you'll be able to pin-point the amount of hot water needed for any given time the shower will be utilized. From there, all you need to do is find a good match - be it a storage type or direct-fired water heater.
  • Mark Evans
    Mark Evans Member Posts: 4
    First Hour Rating- sizing a dhwt
    Tom,
    The First Hour Rating is the peak hour demand for a given installation. In a residence, that will normally be in the morning, but check their schedule. There is a HUD-FHA Table that provides minimum recommendations for average households based on the number of bathrooms and bedrooms.
    For 1 to 1-1/2 Bathrooms
    1 Bedroom
    20 Gallons Storage
    27 K Btuh min. input
    Expected First Hour Draw 43 Gallons
    Recovery 23 Gallons
    2 Bedrooms
    30 Gallons Storage
    36 K Btuh min. input
    Expected First Hour Draw 60 Gallons
    Recovery 30 Gallons
    3 Bedrooms (same as 2)
    30 Gallons Storage
    Recovery 30 Gallons
    2 to 2-1/2 Bathrooms
    2 Bedrooms
    30 Gallons Storage
    Recovery 30 Gallons
    3 Bedrooms
    40 Gallons Storage
    Expected First Hour Draw 70 Gallons
    Recovery 30 Gallons
    4 Bedrooms
    40 Gallons Storage
    38 K Btuh min. input
    Expected First Hour Draw 72 Gallons
    Recovery 32 Gallons
    5 Bedrooms
    50 Gallons Storage
    47 K Btuh min. input
    Expected First Hour Draw 90 Gallons
    Recovery 40 Gallons
    3 to 3-1/2 Bathrooms
    3 Bedrooms
    40 Gallons Storage
    Recovery 32 Gallons
    4 Bedrooms
    50 Gallons Storage
    Expected First Hour Draw 82 Gallons
    Recovery 32 Gallons
    5 Bedrooms
    50 Gallons Storage
    Recovery 40 Gallons
    6 Bedrooms
    50 Gallons Storage
    50 K Btuh min. input
    Expected First Hour Draw 92 Gallons
    Recovery 42 Gallons
    Hope this helps.
    Mark.
  • chris_24
    chris_24 Member Posts: 22
    that seems
    a bit low to me.
    I guess there is an average for everything, but in reality, ask your customers what their needs are, how long of a shower do they take, then based on the heaters recovery rating, you can size your heater.
    I hate running out of hot water, and I am NEVER the first one in the shower EVER!! size the thing according to the needs of the clients, after all we are all about comfort here.
  • Great tables!
    If that 70 gallon tub only has 1 bedroom near it, a 20 gallon tank is big enough?????
    Give me a break.
    Noel
  • Tom_53
    no showers
    Informative tables, but showers are not the the problem. The guy has a 70 gallon tub and wants to fill it with hot water. 30 gallon oil fired unit is not working. The boiler does not have the btu s to suport a large indirect, 60 0r 80 gallons. Other opinions are appriciated.
    Thanks, Tom
  • Firedragon_4
    Firedragon_4 Member Posts: 1,434
    Although we spend an entire book
    explaining the math to do this with in "The Hot Water Handbook', sometimes simple is best.
    With tank type heaters the best rule of thumb is simply to 'calculate all of the capacities of the tubs and figure on a one-on-one gallonage basis. 70 gallon tub, 70 gallon heater.
    That really covers the 80% Rule on cold-water feed, the Btus, etc. it's simple and it works, FACT!
    www.firedragonent.com
  • Firedragon_4
    BTW,
    you could tack a booster system onto that 30 gallon and probably get away with it. Call the guys at TFI-Everhot to be sure, it's their tank.
    http://tfi-everhot.com/
  • Scott Gregg
    Scott Gregg Member Posts: 187
    Right...but
    Using that rule with a Bock 70 gallon also gets you able to fill the tub and support a shower right after filling it!
    One can also set up a Bock water heater temperature to 160* (Even on the 50 gallon unit) and use a mixing valve to knock down the temp to 125* or so. This will keep you from running out by using less hot water during a peak draw. A Bock is built to handle such things.
    There is more than one way to skin a cat.
  • Firedragon_4
    Yup, but
    when comparing heaters make sure that the ratings are based on the same recovery rates. Make sure the rise is the same too, inlet water temperature vs. supply temperature.
  • Tom_53
    final decision
    I glad i have a computer, all this input helped me decide what to do. 1st choice was a 70 gallon oil fired hwh, would not fit. 2nd choice is a 50 gallon aquabooster from the existing 30 gallon water heater. Piped in series for a total storage of 80 gals. I have never tried this but i think it should work.
    PS If it does not work i will let you know.
    Thanks again to all who responded.
    Tom,Long Island
  • Bruce M.
    Bruce M. Member Posts: 143
    On Demand Hot Water Heater
    How about an on demand hot water heater.
  • Jack_21
    Jack_21 Member Posts: 99
    Rinnai on demand
    Should you choose to go gas on this. If the tub is supplied with 1/2" you aren't going to get much more than 5gpm to the tub. If it is 3/4 then that is another matter. A Rinnai 2520FFU will give 4.5gpm at 70F rise. If you are in a tub over 105 you are no longer bathing you are par-boiling. If they want faster fill and have larger supply then you can use two. The advantage to these on tubs is that I have hardly ever taken a bath that within several minutes you didn't need to peak the tub with more HW. With the on-demand you can stay in a hot bath as long as you wish. The customer can enjoy the appliance.
  • Jed_2
    Jed_2 Member Posts: 781
    So, where ya been, Jack?
    We've missed you.
    Jed
  • Dave Yates (PAH)
    great application
    if you do your homework and know the incoming coldest water temp, flow rates to calculate demand and the real GPM rates the units are capable of producing - not the pie-in-the-sky projections some manufacturers are touting in order to gain sales.
    Short rule of thumb: gross input Btu's, multiplied by .82 or whatever the steady-state efficiency rating might be, and divide that by 833 for GPH & then divite by 60 for GPM.
    For instance: 189,000 x .82 = 154,980 Divided by 833 = 186.05 divided by 60 = 3.1 GPM
    Takagi's charts show various incoming water temps & are pretty much dead-on for GPM rates at the temps shown.