Taco twin \"T's\"
Weezbo
Weezbo Member Posts: 6,231
with the Taco Twin "T's" ?
  • Weezbo
    huh?.......*~/:)
  • Kal Row
    Kal Row Member Posts: 1,520
    goto taco-hvac then products/systems/the loadmatch system
  • Kal Row
    to me the bigest advantage of the twin-T...
    over regular closly spaced t's, is that, the twin't is not only flow rate decoupled, but flow direction decoupled as well
    so you can put it into systems where you do flow reversal for system eveness - which is always a problem with close t's, the first set of T's get the hottest water
    with TWIN-T system-a - you need to, but can, reverse the flow for even supply temps,
    with system-b (close-t crossovers on a resverse return) - you set it and forget it
    in the end, i am actually doing this with c.pdf
  • Joe Mattiello
    Joe Mattiello Member Posts: 741
    Taco, Inc.
    Joe Mattiello
    Technical Service Technician
    joemat@taco-hvac.com
    401-942-8000 X 484
    www.taco-hvac.com
    Joe Mattiello
    Taco Comfort Solutions