Probe lwco
kevin coppinger_4
Member Posts: 2,124
steam relacement...The HO dryfired and old WM steamer. I opted for a Smith 8-3 section steamer, Carlin burner and a probe type lwco(hydrolevel CG450) packaged set. I added the MM unimatch feeder. With the cycleguard feature the boiler checks water level after 10 min . of run time. As I was there chcking operation the lwco goes to check the level and instead of a clean shutoff of the burner it does this quick on/off cycling thing for 30 seconds of the burner. The watewr level was high enough so any fluctuation of the water line would not effect it and the probe I checked for crud and it was clean...any thoughts? I have started skimming and adding squick to clean it up better...but I will be back for sure. TY! kpc
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=323&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
lwco
I LIKE TO CHECK THE EASY FIRST YOU DIDNT USE TEFLON TAPE DID YOU? JUST FOR KICKS TRY INSTALLING A SEPRATE GROUND WIRE FROM THE SKREW THAT HOLDS THE CONTROL TO THE WELL AND CONNECT THE OTHER END TO THE BOILER IGNITION CONTROL GROUND OR AT LEAST THE BURNER GROUND0 -
yes I did....
but it was doing this when it was installed from the factory and only had pipe dope on it....I will go back and remove just for kicks...ty,kpc
bring some green wire with you and make sure that control has a good ground just a recomendation0 -
you know it....
was an old system...65yrs...the wire to the old boiler probably does not have the best groung to it......hmm. kpc
Does it have the pre & post purge Carlin control? Make sue the Red wire remains live when the LWC cycles0 -
ok...
it should be since it is factory wired....but mistakes happen...kpc