OO7 circ
If a hundred watt lightbulb uses $.04 worth of electric an hour, how much power would a 007 circ use? Customer is concerned about a primary pump running 24/7. I am not sure of the answer.
Thanks
Andy Morgan
R. Morgan Mechanical, LLC
  • Al Letellier
    Al Letellier Member Posts: 781
    007 draw
    Andy, watts=voltsxamps, so a 007 at 115 volts has a normal amp draw of .7 amps, then a 007 will draw the equivelant power of a 80 watt light bulb. Flow head will vary the actual amp draw of your pump a little one way of the other, but this is close enough to help you win your point.
  • steve_66
    steve_66 Member Posts: 1
    taco 007 power usage
    According to my catalog info, a Taco 007 consumes 0.7 amps at 115 volts, or roughly 80 watts of power. In 24 hours that would add up to 80 watts x 24 hours=1920 watt hours or 1.9 kwh. At our local rate of $0.15/kwh the cost would $0.28 /day. By comparison, a 100 watt light bulb burning 24 hrs/day consumes 100 x 24 = 2400 watt hours or 2.4 kwh. At $0.15/kwh that would be $0.36/day
  • Dave_22
    Dave_22 Member Posts: 232
    Power
    amps rating on pump X voltage(120)=watts X price per Kwh
    for example:
    .7 amps X 120=84watts 84watts= .084 Kwh
    If the rate is 10cents a Kwh then:
    .084Kwh X .10 cents= .0084 cents per hour
    equates to about $6.04 a month.
    Someone let me know if my maths wrong!!!!
  • Mellow_2
    Mellow_2 Member Posts: 204
    circs
    If you have ten circs turning on and off you could burn more electricity than zone valves.........cool how about 14 zones.......
  • Steve Eayrs
    Steve Eayrs Member Posts: 421
    I bet someone has a handy chart out there
    Would be nice to look at the total amps draw and the cost per kwh and get a quick comparision of costs. Would be great to hand out to customers who need more reasons to upgrade, than the obvious 10-30% in fuel savings.
    Anyone want to share the info?
    We all run into those systems with constant operation pumps, that w/ proper i/o reset and other controls could reduce the run times at least in half.
    thanks,
    Steve
  • Ron Schroeder_2
    Ron Schroeder_2 Member Posts: 176
    Low power pumps.
    If you are really looking into power savings, carefully determine your pump sizing. The head in a primary loop is usually low so you might be able to use a Taco 005@.53A, 006@.52A or 003@.42A or even a Laing UC-303B@.3A.
    Laing Inc. and Ivan Labs make DC pumps that are suitable for injection pumps and small to medium loops from 20 watts down to only 5 watts.
    Also there are some very low wattage zone valves like the Taco ESP or the Caleffi thermal actuators at 3 Watts and the Slant Fin Thermal actuators at 2 Watts.
    Ron
  • Uni R
    Uni R Member Posts: 663
    power use
    Hrmmm... $0.04 x 100/1000 = $0.40 per KWH That's some very expensive electricity there. The 007 uses almost exactly 80% as much electricity as that 100 watt bulb. Given a more realistic figure of $0.15 per KWH, that would be $0.012 per hour or about $0.30 / day during the heating season. A 200 day season makes in about $60 annually.
  • steve_67
    steve_67 Member Posts: 1
    handy chart
    I have an Excel spreadsheet that I use to calculate operating cost. An image of the output is attached. I'd be happy to email the spreadsheet to you.
  • Steve Eayrs
    thanks Steve
    I would love to get a copy of your spreadsheet.
    e-mail is eayrs@xyz.net.
    thanks, Steve