Main Vents - Help with Sizing
L. Peck
Member Posts: 2
I would be most grateful if someone would help me properly determine the appropriate size of the main vents on my one-pipe steam system.
My home has two mains. The first is 3.0 inches in diameter, 61 feet long, with a Gorton #1.
The second main is 2.5 inches in diameter, 55 feet long, also with a Gorton #1.
Many thanks for any replies.
Those are some big pipes!
The 3-inch one has about twice the air in it as the 2-1/2-incher. So it needs twice the venting capacity. I would vent the 3-incher with two Gorton #2 vents, and the 2-1/2-incher with one Gorton #2.
These vents will allow the mains to fill with steam in about a minute, and the steam to reach the ends of both mains simultaneously.
www.gorton-valves.com
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Consulting0 -
Thank you Steamhead for your prompt and professional reply.