distance between vent and property line?
hr
hr Member Posts: 6,106
Termination The termination of chimneys or vents equipped with power exhausters shall be located a minimum of 10 feet (3048 mm) from the lot line or from adjacent buildings. The exhaust shall be directed away from the building.
Page 67 of the 2000 IMC, which is the code used around here. Probably is a newer version, check with your local AHJ for their opinion.
hot rod
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=144&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
  • Plumbob
    Plumbob Member Posts: 183
    city follows IMC, not UMC
    Some time ago I asked about this, and someone said that according to the UMC, the vents must be 4ft from a property line.
    This has to do with our neighbor's new furnace, which is venting directly in front of our front door (which is on the side of our Dutch colonial).
    The city says they follow the International Mechanical Code, not the UMC, and there is nothing in it about the distance from the property line. I find this hard to believe...
    Unfortunately, the IMC is not on the web; I'd have to buy a book. So any help is appreciated.
  • don_52
    don_52 Member Posts: 199
    venting
    used to be 3', then 6' and now 10', city ( chicago ) is still working on "harmonizing" these issues between the
    building, fire, plumbing and mechanical codes.
    in the past ( and some still ) do conflict though.
    might check with the "other codes" to see if they
    have a different view on that.
    i.e., local fire code may have greater clearance than
    IMC, and that's what's used as the minimum standard.
    Sec.8, pg. 63 chi mech code;
    18-28-804.3.3 Termination. The termination of chimneys or
    the building.
    this now applies to all buidings here grandfathered or not.
    regards, don
  • Geno_15
    Geno_15 Member Posts: 158
    Don't forget
    the city has to follow national building codes, they are the minimum, a local building inspector can toughen existing regs but cannot soften them.
  • Plumbob
    Ok, thanks!
    Thanks for the quick and knowledgeable help. With renewed confidence I will pursue the matter further.
  • jim lockard
    jim lockard Member Posts: 1,059
    Zoning
    Look at your local zoning laws, you may find some relief there as well. J. Lockard
  • Jim_47
    Jim_47 Member Posts: 244
    Venting
  • Jim_47
    Venting
    In reference to Venting your neighbor's appliance near your front door, You may look at NFPA. I do not have my copy here so I am going by memory and not the exact wording.
    There is a section as to venting with regards to near a window, door and sidewalk. I am sure you can interpret it as any building not just the building that is housing the appliance.
    I cannot believe that there is even someone that would install with no regard for human life and safety?????
    Have you questioned the building inspector or fire inspector? keep us all posted on this one.
    I refused to install a power vent (on an old farm house)for an oil Hot Air furnace because it could not be installed corrcetly. (To close to windows and main front door as well as blowing across the main side walk.) Homeowner told me not to worry about those silly charts and diagrams I showed him. I told him that I would not be able to live with myself if there were ever an injury due the installation being incorrect.
  • jim lockard
    There jim
    those silly little charts and diagrams spoil everyone fun.
  • Ken_8
    Ken_8 Member Posts: 1,640
    3 feet from any window or door,
    10 feet from the property line.
    I wonder however about dryers and their vents. Same dynamic, just not a "boiler."
    The code is silent on dryer venting. Then again, who'd run their dryer 20 hours a day all winter long...(:-o)