Condensate hot water heating.
Jim S
Member Posts: 82
We recently installed a new steam boiler in a residence which had an existing condensate hot water loop on the first floor.
As part of the new install we re-connected that loop and added an additional zone on the second floor.
we used one pump and two zone valves, and we didn`t use a heat exchanger ,now we`re getting calls for no heat on the second floor.
Both zones together don`t add up to much of a btu load so i don`t think that`s the problem,i`m just wondering if having two zones on two different floors is a no-no.
Two zones are fine.
Did you install the boiler bypass line?Retired and loving it.0 -
yup.0 -
did you try
opening the zone valve and turning on the circulator? It could be you have a bad zone valve. I have used circs on multiple floor job's and never had an issue there..0 -
Went back today,turns out the water was passing through the boiler without picking up enough heat,had to relocate the supply to a tapping higher up on the boiler rather than off the bottom.
Seems kinda strange though,they were on opposite sides of the boiler,diagonal to each other but it still wouldn`t work.
What a b...h getting the damn plug out though,but that`s another story.0
- 167 Indoor-Air Quality