W/M Plus 100 question
Phil_6
Member Posts: 210
I just took over a job to finish where they have a Weil Mc Lain Plus 100 indirect water heater connected to the boiler. I usually don't use this brand of water heater, but it seems to work great except for the water temperature of the domestic water shoots way up to 170-180 degrees no matter what the thermostat on the tank is set at. The piping and wiring is all pretty straight forward, heater is wired to an Argo relay which starts the circ and boiler. I changed the thermostat assembly like the Weil McLain tech guy suggested but I guess he was wrong. Still happens. Any suggestions?
Thanks, Phil
Thanks, Phil
inderect check
have you checked the piping? are you getting unwanted heat migration through the inderect water heater loop? is there flow checks installed on the supply and return lines.0 -
wiring?
If you checked the above:
Something could be wired funny, or the Relay is shot - causing the pump and boiler to stay on even though the aquastat is satisfied.
Check the wiring and relay. You may have some backfeeding going on there.
Mike0 -
wiring
every thing appears as it should be. I can stand right there and watch it shoot right to 170 or so and the relay shuts off.The thermostat on the water heater clicks the relay right on and off. Just not at a low enough temp.0 -
Check for a
properly sized pump for the tank. The +100 needs 22 gpm @ approx 2' of head. That means 1 1/2" pipe. Can't cheat on this puppy. Funny things will happen.
PLUS 100
> suggestions?
> Thanks, Phil
PLUS 100
i install a lot of these tanks and they all seem to stack a lot of temp. I certainly hope you have a good mixer on that hot water line.
I HAVE PUT IN MANY +40'S AND HAVE HAD SERVICE CALLS ON +100'S. MY GUESS IS MAYBE THE FLOWCHECK OR ZONE VALVE (EITHER/OR) ISNT CLOSING FULLY, OR MAYBE THAT EXTRA DIP TUBE THAT COMES WITH IT MIGHT HAVE BEEN PUT IN THE HOT SIDE BY ACCIDENT. AND MAY NOT HAVE ONE ON THE COLD SIDE ( IVE SEEN SOME REAL BEAUTS) HOPE THIS HELPS
Thanks
Some one else installed this equipment. Judging from the sloppy work around the house, anything is possible. I think I'm going to tell the cust we need to disconnect it, inspect it and re-install it with a mixing valve. I hope they'll go for it.
Phil0
- 167 Indoor-Air Quality