Pressure testing of hydronic equipment in the field
Is there an industry standard for testing hydronic equipment prior to operating the system? I see that Runtal radiators have a test pressure of 110 psi and an operating pressure of 85 psi max. How long should it be tested at 110 psi?
  • Dan Peel
    Dan Peel Member Posts: 431
    Example
    Most of those test numbers are factory test pressures of individual components. On system air pressure tests we use 40-50lb (isolation of relief required) over 24hrs or for hydrostatic testing 25lb. With many systems it's trial by fire and repair as required, especially in season. Enjoy....Dan
  • hr
    hr Member Posts: 6,106
    If the boiler is
    in the loop being tested you may be limited to below 30 psi, as that is where most reliefs trip.
    For radiant tube only I like 100 psi. It shows a leak quickly at that pressure.
    Copper and other piping should handle 45 or so. Check the listings on zone valves and other components first.
    hot rod
  • ed_19
    ed_19 Member Posts: 14
    We are usually required to test to 3 times the working pressure for 24 hrs. A lot of the time we test to around 130lbs. This is due to the fact that that is our compressors highest setting. And remember pressure will change with temperature.
  • pressure test
    We usually test the new boiler at 1 1/2 times the maximum working pressure (or the relief valve pressure). We will hydro-test using water, not air to 45 PSI on a 30 pound boiler, 22.5 PSI on a steam boiler. We always hydro-test after any major repair (Re-tubing for example). The boiler and relief valve are isolated from the rest of the system. A leak will usually show up instantly or in a very short time. I would not try this on an old systems piping or you may have more work then you banked on.