insul-tarp

Smathers
Smathers Member Posts: 1
I'm considering using insultarp under the concrete slab in a walk-out basement. Has anyone used insul-tarp? Do you know of any pros/cons? I'm concerned with it's performance over time since it's a relatively new product as well as it's actual insulating value.

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • Constantin
    Constantin Member Posts: 3,796
    Do a search...

    ...this topic has been beaten to death on a number of occaisons. The upshot, IIRC, is that it has a R value of about 1 below ground, i.e. it's better than nothing, but barely so. ASHRAE has also published a comprehensive guide on sidewalk snowmelt options, so $60 and a bit of reading later, and you should be good to go.
  • Mike Kraft_2
    Mike Kraft_2 Member Posts: 398
    Low E Shield

    As Insultarp, Low E is user friendly.Unlike Insultarp,Low E has a true and reckognized "R" value.It is easy to lay,does not tear at all and can be cut around structual members ie: lolly columns etc.It also is an approved vapor barrier.Try it you'll like it.:)

    http://www.low-e.com/Products & Services/Product Line/Slab Shield/Slab Shield.html

    cheese
  • Brad_9
    Brad_9 Member Posts: 29
    aluminum film insulation

    I find the reasoning behind the Low E shield to be faulty. "Foam board draining away heat"??!!. Although there is a difference between r-values of different foams, the range is from about 4 to 8 per inch with extruded polystyrene at 5 per inch. From what I've seen of polyethylene foam I expect it's near the lower end of that range due to the large cells in the foam. That puts it at about R-2.5 at most at 1/2" thick. Having the aluminum in the center will have virtually no effect on r value in this application. There's no radiant heat to reflect when it's in contact with anything except air. In this case it has foam glued to it. I think everyone should realize that it takes a certain thickness of foam to do the insulating under a slab. No easy outs.
  • Mike Kraft_2
    Mike Kraft_2 Member Posts: 398
    I agree

    about the aluminum.The slab shield I believe has a R3 rating.It's been awhile since I have installed it.Depending on the earth under your insulation this is enough IMO.The edge loss is where the beef is important!For the edge 1" minimum extruded polystyrene.I requsted a bit more detail from LowE and am waiting.
  • Hoist
    Hoist Member Posts: 5
    Where does the water go?

    I'm installing a 1600sf snow melting system. Where is ithe water supposaed to go when you seal underneath the cement with insultarp? I have a 60ft long driveway sandwiched between 2 houses. Rain and melted snow going through the pourous cement and expansion joints will need somewhere to go underground. I don't want that to be my foundation or my neighbor's foundation. R-1 to R-3 insulation doesn't seem worth a wet basement or damaged brand new cement. Any comments help on this issue would be appreciated.