Feet of head to PSI conversion
S Davis
Member Posts: 491
Anyone have a conversion chart for feet of head to PSI?
Thanks
S Davis
Apex Radiant Heating
Thanks
S Davis
psi
height x .4340 -
Pump Head
What I need is conversions for pump head to PSI and I think you need conversion charts depending on system temp and fluid, glycol etc.
S Davis
Apex Radiant Heating0 -
(feet of head Divided by 2.31) x specfic gravity= PSI
From my Grundfos wallet card.
hot rod
Thanks
Thank you thats what I was looking for.
S Davis
Hold the phone!
The conversion of feet of head to psi IS dependent on the specific gravity of the fluid. The lower the SG, the higher the column of water required to produce 1 psi. This can be critical when using pump head to go to the curve and determine flow. The ASHRAE Applications Handbook has a chart in the chapter on Testing, Adjusting and Balancing.0
