Steam heat for new construction
Ken C.
Ken C. Member Posts: 267
Someday, I may build myself a house, and I would like to heat it with steam. I grew up in a house with steam heat and the old cast-iron radiators, and think it's the best type of heat out there. Of course, most new houses today use scorched air or hot water systems, which undoubtedly cost less to install than a steam system. But, do any of you know any new houses that were built with a steam heating system? How much more expensive would it be than, say, a hydronic system with fin-tube baseboard? Can you even buy the traditional, cast-iron steam radiators today? Are there other (more modern) styles of steam radiators that the wife wouldn't ojbect to?
  • You can still do it.
    I have built one, Mad Dog just built one, Steamhead built at least one, and many more have been done recently.
    They are pretty expensive to maintain, but just as comfortable as you remember them.
    Radiators will have fewer sections today, because we insulate walls and close windows in the winter.
    Here's the instruction manual. It's very good.
    http://www.heatinghelp.com/shopcart/product.cfm?category=4-25
    Noel
  • Christian Egli
    Christian Egli Member Posts: 277
    Here is a brilliant man
    Steam is not popular with modern home builders but I think that is because they are under pressure to provide the lowest initial cost and that's perfectly fair. So you have to choose steam, it is not odd at all and I should encourage you.
    Everything needed is still available either brand new or antique, the part that is more difficult to find is the installer that knows how to do it. There are reports of new homes with steam on this site, wait for Steamhead's reply.
    Radiators come in designer colors nowadays, your wife should love them and they'll be the hottest thing in your home.
    Component costs are similar to hydronic but piping costs might be higher because of the larger sizes than with water and depending on the complexity of the home.
    Keep in touch until the time you design a home around your steam heat.
    Best regards to you and your wife.
    Christian Egli
    Steamhead Member Posts: 17,932
    It's feasible
    if you want good comfort and efficiency in a system that won't freeze and burst as hot-water can in a power failure. Assuming similar boilers and that both systems are in good shape and insulated well, steam is about as efficient as hot water.
    Noel's (and I agree with Christian, Noel is one of the best) company, Slant/Fin, still sells fin-tube baseboard that can be fitted with steel-pipe elements that work great on steam- the Multi-Pak 80 series. I've used this and it's a good, durable product. The only caveat is that it must be installed with a steam supply and condensate return line (two-pipe system). One-pipe doesn't work too well with baseboard.
    The next step up in comfort (and cost) is cast-iron baseboard, as made by Burnham, Weil-McLain and others (unfortunately, Slant/Fin's is not rated for steam). This also works best on a two-pipe system.
    Cast-iron radiators are still made, but are more expensive than baseboard unless you get them second-hand. But they will work with two-pipe or one-pipe steam. And of course there are newer "decorator" radiators out now- I think Alan Forbes, the California Radiant Genius has used them with much success.
    One variation of two-pipe steam, the "Orifice Vapor" system, has the fewest moving parts of any water-based system I know of. This means there's less to go wrong, and maintenence is less. It also operates on about a half-pound of steam pressure, so it is very quick. BTW, it was on this type of system that I used the Slant/Fin Multi-Pak baseboard (since it was similar to the units already in place), but you can use any type of heat transmitter with it.
    Installation is more labor-intensive since you must use black steel threaded pipe on any line that carries steam. But once you get the hang of working with this pipe it's not bad. Copper can only be used on lines that do not carry steam.
    Several of us, including Noel, Mad Dog, Dan Foley and myself, have installed steam from scratch. We all started with a heat-loss calculation, as with any system. With a well-insulated building the radiators or baseboards will seem tiny, but they will get the job done.
    Tell us more about the house you plan to build!
    Consulting
  • Jeff Lawrence_24
    Jeff Lawrence_24 Member Posts: 593
    What price is your comfort?
  • Jeff Lawrence_24
    That's it, simply put.
    Do you really want the scorched air throwing out all the stuff on you or the gentle convection currents warming the air?
    Sure, forced air can give your cooling, but look at 'basic' physics. Warm air rises and cool air falls. You really want the heat at the perimeters of the house on the lower level of the floor amd the cooling at the high perimeter of the house.
    I love my bride of almost 20 years, but our decorating savy is really different.
    J.
  • From 2 of the best
    steam experts - Noel and Steamhead , their advice is gold .
    Personally I never installed a steam system from scratch , but I have replaced hundreds of steamers and saw all kinds of pipework . Much of it takes alot of space in the basement , so you would want to plan the layout very carefully to keep the proper pitch and leave room if you want to finish the basement . Nothing hurts more than banging your head on a low hanging dry return .
    How would you think this system would work in the long run - series 80 multipak connected by an all copper supply and return system , all type L , using the strongest solder of choice ( maybe brazing also ) , connected to a steel steam boiler ( if they make em still ) ? Call it steam on a budget . Feasible ? Or just plain dumb ?
  • Weezbo
    Weezbo Member Posts: 6,231
    Steam may be an option in some muni's...
    some cities have steam laid on....Woop There it is:) We have stem in Our burg in places:) can you dig it?:)
  • DaveGateway
    DaveGateway Member Posts: 568
    Not to get any of the experts mad
    But I was under the impression that all steam boilers only get to 80% efficency. Would it make sense to even consider when modulating/condensing technology exsists puting out over 90% efficencies? With the options of zoning and the added safety for children of not having scalding hot radiators in the room, I can't see why anyone would even consider steam. I grew up in a stuffy dry steam heated home and I think my current HW BB house is better. I have great respect for the guys here who can maintain steam systems and have corrected systems that have increased the comfort, fixed noise problems, etc. But other then the non-freezing pipe advantage, I think it would be wrong to suggest steam over a more effcient and well designed HW system for new installs.
    luketheplumber
  • Kal Row
    Kal Row Member Posts: 1,520
    just remember that
    steam heat is a lot more efficient as radiant than as conductive/convective – if you have a steam radiator by a window, you can sit across the room with the window open on a zero degree day and feel comfortable, I am sure that there is many a public school kid out there with just such a memory of having sat in class with the windows open, and still roasting, that’s the problem with the “old double-hung zone valve” it may let the hot air out but it don’t stop the radiant heat,
    anyway, plan on have all the radiation in plain sight, by windows, or near the TV where is can radiate on viewers, and, since dark flat objects are better infra-red emitters, than shiny/smooth objects – don’t plan on having them look to pretty – unless of course you get creative – like having hidden radiators – reflect off shiny walls – trust me it works – light is light – if you point an infrared temp gun at a radiator through a mirror “whad-ya-git”, infrared energy of course – though, you do have to factor in, the increased distance to the radiation and the resultant light dispersion
    having said that – if you set up right – you fuel bills based on current costs for a normal run-o-the-mill sized house, should be 140-180 per month – it doesn’t get better than that!!! – real world experience has shown that, fully condensing hydronic radiant is NOT I repeat IS NOT cheaper to run!!!
    If you do it wrong, it’s hell – I have an institution in my neighborhood that had 1million btu of radiation and a 1 million btu boiler, now the building only has an ibr load of 670k so it was already wrong, then the boiler died and they replaced it with 1.5million btu boiler and they also remodeled and recessed the radiation into the walls, – so now – the whole system short cycles on 40seconds and is basically useless even though it’s costing them 5000 per winter –
    people just don’t like black radiators on the wall – even though it’s provides the best heat – so if you wife doesn’t want exposed radiators, don’t even think about it – go for the next best thing, put aluminized sub floors onto floors, or ceilings or walls – drop in pex tubing, hook it up to a condensing boiler and have a nice day
  • Kal Row
    just remember that
    steam heat is a lot more efficient as radiant than as conductive/convective – if you have a steam radiator by a window, you can sit across the room with the window open on a zero degree day and feel comfortable, I am sure that there is many a public school kid out there with just such a memory of having sat in class with the windows open, and still roasting, that’s the problem with the “old double-hung zone valve”, it may let the hot air out but it don’t stop the radiant heat,
    having said that – if you set up right – your fuel bills based on current costs for a normal run-o-the-mill sized house, should be 140-180 per month – it doesn’t get better than that!!! – real world experience has shown that, fully condensing hydronic radiant is NOT I repeat IS NOT cheaper to run!!!
  • Boilerpro_3
    Boilerpro_3 Member Posts: 1,231
    A couple things to think about
    Boiler AFUE is only a small part of overall system efficiency. Modern hydronic systems require electricaity to operate and most condensing boilers require alot of it for the large pumps they need for high head heat exchangers ( the Dunkirks and Hydrotherms are the only exceptions I'm aware of). That number is not incluced in the AFUE rating.
    Ther is also the obvious issue of distribution losses, where hot water probably is better.
    However, how the heat emmiters react with the spaces they are heating is probably more important than these other factors. Any low mass system (convectors) without input modulation is going to send pulses of hot air to the ceiling, increasing heat loss due to higher delta tees at exterior surfaces and causing increased infiltration...the biggest heat loss in newer homes. You can put reset on your baseboard system to help this, or simply use high mass emitters to thermal flywheel the input pulses.....use cast iron rads on steam.
    Also delivering radiant heat, which cast iron radiator systems deliver in part and convector very little, allows lower air temps with the same resulting Mean Radiant Temp, allowing lower thermostat settings all winter, further reducing operating costs.
    As to zoning any steam system can easily be zoned room by room, so I see little benefit to hot water here.
    If you take into account the increased electrical usage of hot water and decreased system efficiency due to differences in radiant heat delivery, the actual overall energy usage of a convection hot water system, and a steam system using radiators is probably about the same.
    Now if you were using low temp radiant with your hot water system, and convectors with your steam system, this would likely greatly alter the results in favor of hot water.
    Its not just one heating fluid medium versus the other, but how the fluid is used to deliver heat to the spaces heated that really can make a difference.
    Boilerpro
    Copper pipe
    would be useful on return lines, but I'm not sure any soldered or brazed joint would survive for long on steam lines.
    But the headroom problem can be solved.... if you run your steam main perfectly flat, and take your runouts off from the bottom at a 45-degree angle and drip each one to the wet return, each will drip the main and it won't bang. This appears in one of my Dead Men's Books but I forget which one.
    Consulting
    And
    I'm not sure what the surface temp of a rad would be with steam at only a few ounces in it. That will be something to check with my infrared thermometer the next time I start up a steam system.
    Many hot-water systems built after World War II, however, use pressurization to get hotter water without boiling. In some cases, these approach or exceed steam temperatures. So these radiators would not be any cooler than steam radiators except in very mild weather. And a condensing boiler would not condense very much on such a system either.
    Consulting
  • Ken C.
    Thank you for your interest
    To answer your question, Steamhead, I'm nowhere near ready to build a house at the moment. Realistically, it would be five years from now, best case. The house would be located in a rural area with cold winters (in other words, where land is still cheap). Besides the quality of steam heat, another reason it's attractive is that power outages and freeze-ups are less of an issue with steam systems than hot water systems. While I would pay more in materials, that would probably be offset by doing much of the installation myself (I'm a soon-to-be journeyman plumber and have cut and threaded my fair share of black pipe). You mentioned several options for the radiation, although I'm still partial to the traditional cast-iron radiators. Those would be a tough sell to my wife on a new house, although if we end up buying an old farmhouse instead of building new, I'm sure she would learn to live with the old radiators. Being a plumber, the higher maintenance of a steam system doesn't bother me. It's good to see there are still some new residential steam systems being installed. It's becoming a lost art, not too many guys in the plumbing/heating trade around my age (early 30s) seem to have much interest in working on steam.
  • jack_22
    jack_22 Member Posts: 5
    New steam heat
    Steam heat in a new building is a romantic idea. To add to the nostalgia, be sure to also use a wood or coal hand fired boiler while you're at it. Don't plan on going anywhere until spring. Have a WONDERFUL wintr.
  • Christian Egli
    Everybody in this post is coming up with the good arguments, it is a delight.
    Here is what I have to think about the surface temperature. The radiator all full of steam at, say, 5 ounces (which condensates at 213F) should measure no more than 213F. The supply pipe will measure that for sure unless there is a big pressure drop at the valve.
    But if the radiator itself goes into a slight vacuum you'll see a small drop.
    That's the theory, now prove me wrong with the facts. It's always the way it happens.
    Can you also install a pressure gauge on your radiator, just to let us know?
  • Kal Row
    ok here goes
    it takes one British fellow with a tweed suit, briefcase , bowler hat, and umbrella, to raise an English pound of water on degree, but at 212, it takes another 970 of them British fellas, to turn the same temp water into “shteem”, so the total number of brits working for you in that pound of water is 212+970=1182, which would be the temp, you would have to get a pressurized hydronic system to, on order to possess the same energy, – now you might ask who cares – we will just circulate more btus over from the hydronic boiler, problem is, that takes time, and energy, and if you wanted to open a window and let some fresh air in at the same time, the hydronic system just couldn’t keep up, where as the steam, just keeps condensing and maintaining the same 212 infrared energy steady – it’s a thing of beauty – this efficient energy transfer mechanism mitigates the losses from it’s boiler not being a fully condensing type – though there is no reason, that a secondary heat exchanger, couldn’t be put on the flue, to recover energy for hot-water based loads
    steam only falls apart, when you only want to heat a small section of the house at a time, for such a load, even modern radiant is no good, neither is central forced air, for that, you need a hydronic system with a fan coil blower per room, each with it’s own tstat – and you can uses that for cooling too with a liquid chiller
  • Kal Row
    ok here goes
    Like Dan says, it takes one British fellow with a tweed suit, briefcase , bowler hat, and umbrella, to raise an English pound of water on degree, but at 212, it takes another 970 of them British fellas, to turn the same temp water into “shteem”, so the total number of brits working for you in that pound of water is 212+970=1182, which would be the temp, you would have to get a pressurized hydronic system to, on order to possess the same energy, – now you might ask who cares – we will just circulate more btus over from the hydronic boiler, problem is, that takes time, and energy, and if you wanted to open a window and let some fresh air in at the same time, the hydronic system just couldn’t keep up, where as the steam, just keeps condensing and maintaining the same 212 infrared energy steady – it’s a thing of beauty – this efficient energy transfer mechanism mitigates the losses from it’s boiler not being a fully condensing type – though there is no reason, that a secondary heat exchanger, couldn’t be put on the flue, to recover energy for hot-water based loads
  • Kal Row
    ok here goes
    Like Dan says, it takes one British fellow with a tweed suit, briefcase , bowler hat, and umbrella, to raise an English pound of water one degree, but at 212, it takes another 970 of them British fellas, to turn the same temp water into “shteem”, so the total number of brits working for you in that pound of water is 212+970=1182, which would be the temp, you would have to get a pressurized hydronic system to, on order to possess the same energy, – now you might ask who cares – we will just circulate more btus over from the hydronic boiler, problem is, that takes time, and energy, and if you wanted to open a window and let some fresh air in at the same time, the hydronic system just couldn’t keep up, where as the steam, just keeps condensing and maintaining the same 212 infrared energy state – it’s a thing of beauty – this efficient energy transfer mechanism mitigates the losses from it’s boiler not being a condensing type – though there is no reason, that a secondary heat exchanger, couldn’t be put on the flue, to recover energy for hot-water based loads – and indeed there are systems that do so
    Steam, only falls apart, when you only want to heat a small section of the house at a time, for such a load, even modern radiant is no good, neither is central forced air, for that, you need a hydronic system with a fan coil blower per room, each with it’s own tstat – and you can uses that for cooling too with a liquid chiller
  • Boilerpro_3
    I definitely go Radiators
    Convectors, shich have very little mass,will tend to act alot like forced air with steam.... They produce pulses of hot air that race to the ceiling when the steam heat up the convector. The radiator heats more slowly and absorbs the heat of the steam and evens out these pulses...improving comfort and efficiency.
    Also, in a new home the radiators would be very small since the heat load is small. Piping would probably be pretty small too. A typical medium sized bedroom would only need about 12 EDR or a 3 section, 3 column radiator 38 inches tall.... total real estate needed (including space for valve) would be less than 1 sq ft.
    Boilerpro
    Boilerpro
  • Kal Row
    actually not quaint in commercial plants
    where steam is used for everything from heating to cooling (via steam jet venturi vacuum chambers) to cleaning - it's light , self propelling, and doesn’t freeze at plant extremities when off (the returns in these plants are all pumped into central holding/feeding tanks - so they are dry too)