Hissing air vent after boiler shuts down
Options
chuck_6
Member Posts: 107
During the winter, in one of the upstairs radiators, about 5 minutes after the boiler shuts down there would be a hissing type sound coming out of one of the air vents. It's a free-standing radiator, is pitched properly and there is a vent on the main, and the air vent itself works properly. Any ideas why there is a hissing type noise. I'm just a homeowner, so please explain in simple terms.
0
Comments
-
Sounds as though
you have a steam system (vs. hot water).
When your boiler turns on, the steam that's made in the boiler pushes air out of your main and radiator vents.
When your boiler turns off, the steam collapses and sucks air back through the vents. That's what you are hearing and don't worry, that's how your system is supposed to be working.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Alan's right
but you might want to check for uninsulated steam piping, which will make the steam condense and collapse faster and make the whistling louder.
Insulating steam piping will also make the system heat faster and use less fuel. You can't lose by insulating.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 114 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements