Florescent light heat load
helgy_2
Member Posts: 14
Does anyone have a web sight or other good information sourse were I could find florescent heat loads. I'm in the process of sizing a comm. job that has a greater number than usual. Any information would be great.
Thanks, Helgy
Thanks, Helgy
The catalog should list the lamp Watts and number of lamps per fixture. Add some for the balast (15%) and add 'em up. Total watts x 3.41 = BTU/Hr.
Having said that, if you need exact numbers, post the type of lamp (T-8, T-12, etc.), the length of the lamp, the number of lamps per fixture, the type of balast (electronic, magnetic) and post again. I can get you real close.0 -
Woudln't power factor of the ballast also be significant in the ballast loss calculations? Doesn't a portion of tht also become heat in the ballast and wiring?
Matt0 -
Hoboy...
You're gonna need a sparky for that answer. I'm just an airhead. But the power factor would be included in the balast multiplier. The lamps, of course, don't have a power factor.0 -
ASHRAE Fundamentals
The ASHRAE Fundamentals book has formulas for this in the cooling load chapter (Chapter 33 maybe?). I am out of my office, so I can't look it up right now, but it includes factors for number of hours per day that the lights are on, whether the fixtures are ventilated to above a suspended ceiling, efficiency of the ballasts, etc..0