Advice for temp. elec. heaters
GW
Member Posts: 5,184
Hi guys,
We have a pretty big system swap happening next week. Big dollars. I need to keep the house at least from freezing here in Massachusetts. Design heating is just below 80,000. Does anyone have a rule of thumb how much wattage I should set up for temp heat?
Is there any heaters I want to stay away from? Any that I want to look for?
Oh, the house is vacant.
Thanks,
Gary
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=171&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"</A>
Thanks,
Gary
Wattage
You get 3413 btu/hr per 1000 watts. Find out how many btus you need at the temp difference you expect this week. I usually shoot for aboutr 45F indoor, it gives you a safety margin for pipes in exterior walls and to keep plaster form being damaged.
Boilerpro0 -
HEAT
At 72 indoors and 0 outside, I need 74,037. At 45 indoors, my Elite program is saying 46,272. This equals 13,557 watts, if I did the math correctly.
Thanks,
Gary
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
that's 10
1500 watt heaters, that seems do-able.
Is there any dangers I need to know?
Gary
you have 208V or 240V?
Use 240V portables at say 4kW (20A circuit) to 5kW (30 Amp circuit) each so you're looking at 3-4 heaters -- note at 208 a 240 heater will give only 75% output, e.g 3.75 kW vs 5 kW, or even tack up some electric baseboards. Depends on what's readily available for power. With 10 120V heaters you'll need 10 seperate 15 or 20 A circuits (but you may have these vs. 3-5 240V ones w/ receptacles.0