gfa furnase running incorrectly
RICK_15
Member Posts: 3
Need some good ideas about whats going on. Arco Aire furnase 1992, 90 plus efficent.Starts a cycle then flame shuts down after 1 or 2 minutes,ehaust fan stays running then it starts ignition start up a second time and then runs threw the entire cycle correctly to end. What can Ido to fix?
gfa problem
sorry to say there is nothing you can do you need to call for service
sounds like
The inducer pressure is dropping. Check venting, inducer wheel, and pressure sensing port.
Good luck.
Mike0 -
similiar...
Had a system do this..found that the venting had a dip in it that was trapping water...used a hanger to pull the vent back into a straight line, which allowed the built up water to drain in to the pump and have never been back...
stay warm..:)0 -
Cleaning
I would start by cleaning the trap, cleaning the port on the inducer draft. Have you hung your Mag gauge on the on inducer draft fan and checked the pressure? Assuming closed combustion have you tried to run the machine with the combustion chamber open ? How's the flame sensor? is the donut or seal/gasket damaged for the IDF? Best wishes J. Lockard0