power unit
Options
on a number of things. I would suggest you go to the bar above posts and click on search the type in "pilot outage". You will get some good info. Also a search on just "Thermocouples".
A quick answer to your question is that you need an adapter to be able to check the millivolt drop across a power unit. If you will e-mail me I will get some info to you on this subject.
A good thermocouple should give about 25 to 30 milivolts output (it is called an "open circuit" reading).
A "closed circuit" reading should be about 1/2 of the open circuit 12 to 15 millivolts.
The drop out reading should be 6 or less, this is done by blowing out the pilot.
Again in order to be able to do this you need the adapter.
A quick answer to your question is that you need an adapter to be able to check the millivolt drop across a power unit. If you will e-mail me I will get some info to you on this subject.
A good thermocouple should give about 25 to 30 milivolts output (it is called an "open circuit" reading).
A "closed circuit" reading should be about 1/2 of the open circuit 12 to 15 millivolts.
The drop out reading should be 6 or less, this is done by blowing out the pilot.
Again in order to be able to do this you need the adapter.
0
Comments
-
power unit
Is there any way to check the power unit that holds the safety gas valve open in a gas control valve when it is not inslalled in the boiler? Also what should the milivolt reading be on a good thermocouple when it's holding open the safety gas valve? Thanks. J.D.0
This discussion has been closed.
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 167 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements