Flowvalve before the circ ?
I thought the upstairs zone piping was gonna be tighter than how it came out , so I installed the flowvalve upstream of the circulator . Is there any problem piping it this way ?
I changed the piping 3 times trying to keep some clearance to remove the top for cleaning , which can be done as it is . The other pics are the old Low York , and one pic shows a hairline crack in the hood - almost a serious situation .
  • Bill Nye
    Bill Nye Member Posts: 221
    RON,
    With all of those tight spaces you should be using the Taco IFC's or the Grundfos. Would save a lot of room.
    It will "work" but the pump will try to suck the flocheck shut before the water starts to move every time there is a call for heat. It would be better after the pump but oh well , it's done...............
  • hr
    hr Member Posts: 6,106
    Any flow restriction
    on the inlet side of a circ will lead to a potential cavitation problem.
    I agree a circ with intergral check should be in your bag of tricks!
    hot rod
    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"
  • Bill and Hotrod
    Thanks for the info . I had to install the flowvalve 1st once before , as well as today , and it worked good . Now that you both mentioned them , the Taco IFCs woulda fit in there nice - I tried to stand a circ and flowvalve upright and was 3 inches too high . I tried talking to the higher ups about the IFC circs , Taco 007s with a built in relay , pex for long runs of domestic water or heat lines , pressure reducers and backflow preventers with sweat ends .... , sometimes you get so set in your ways it's hard to change . I'll keep trying though . Thanks guys .