Burnham Jubilee
Robert O'Connor_4
Member Posts: 88
Am I corrrect in assuming this is a dry base boiler with a wet back? How would you handle replacement of the combustion chamber? It is oil fired.
Thanks
Robert
Thanks
Robert
Hi Robert, You sure found a fun one to work onYou can still get the chamber for that I believe if not you can replace it with a quick fire equivalent. you'll need to remove the jacket and of course the burner then you'll see that the front section of the dry base comes off. Out with the old in with the new and don't forget the high temp silicone!
depending on how bad it is I would plan on spending a minimum of a half day there. That is including a full brush and vac that may as well be done while replacing the chamber.
Happy New Year Brother!
Your friend in the industry,
Alan R. Mercurio
Oil Tech Talk0 -
Combustion Chambers
for the Jubilee Series Boilers should still be available from Rex Roto Corporation. There are others that you may be able to adapt to fit, but Rex Roto's should be exact based on the model number. They also seem to be very heavy in comparison to other products. Hope this helps.
www.rexroto.com/
Glenn Stanton
Burnham Hydronics0 -
Thanks Glenn and Alan
Thats good information to know Glenn I never heard of them before. I do like chambers to be as subtsatial as the OEM
Happy New Year to you both0 -
Jubilee
This is a wet base cast iron sectional boiler. Weights a ton. No problem, I think, to put a chamber in it, but you may find that the chamber volume is more than you really want or need with a modern burner. I did one with a moulded chamber sitting in the middle of the floor.
am0
- 86.7K THE MAIN WALL
- 56 Biomass
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 159 Indoor-Air Quality
- 69 Pipe Deterioration
- 946 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 43 Industry Classes
