Combustion air deprivation question.
Firedragon_4
Firedragon_4 Member Posts: 1,434
  • JohnNY
    JohnNY Member Posts: 3,341
    What symptoms have you seen that indicate a deficiency in boiler room make up air?
    What is the rule-of-thumb for sizing air intake?
    Where will your rule-of-thumb not apply?
    What is the textbook formula?
    Thanks to all.
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
  • Bob_19
    Bob_19 Member Posts: 94
    I would say
    one of the biggest is creating a negative pressure in the boiler room. If you try to open the boiler room door and you have a hard time then you could have a problem.
    By starving the burner you will have combustion and draft problems. Spillage of gases of combustion could occur.
  • Guy_5
    Guy_5 Member Posts: 159
    Lack of combustion air
    If this is an oil application, soot is almost always an indication of air starvation. That and nuisance no hot water/ have to re-set calls and dirty cad cell eyes on units with clean fires. One other consideration is whole house fans. Folks have a habit of trying to draw 500cfm of air out of their house without allowing an equal amount in. Unfortunately the difference usually comes down the flue and through the heating appliance. Even a clothes dryer can starve an area of air-all that air blowing out has to come from somewhere. I won't even start on the lint issue. As a matter of fact I try to avoid the entire laundry issue in general, but for different reasons.
  • c-rex
    c-rex Member Posts: 48
    combo. air
    seems to me one square inch per 10,000 btu of input, but check the specs on the equipment hand out. By using a blower, you can get a smaller hole in the wall and more control over the air, but it must be interlocked to the equipment. Again, check with the mfg. to get it correct.
  • Wayne_12
    Wayne_12 Member Posts: 62
    1" sq per 1000 btus
  • John@Reliable_4
    John@Reliable_4 Member Posts: 101
    No rule of thumb..............
    1 sq. inch per 1000 BTU per hour = 140 sq. inchs per gallon of oil. Bacharach has allot of good information on thier web site about this, Hope this helps John@Reliable
  • Jack_23
    Jack_23 Member Posts: 153
    Comb air
    It is 1 sq'/1,000btu input...but...That is 1" of FREE AREA, meaning that a 10x10, due to the material of the grill itself will yield a NET area of about 65-75%, depending on the grill type. All grill manuf publish the free area info on their specs. Try www.tjfans.com
  • JohnNY
    Thank you for your replies...
    Where may this information be found? I need to reference the source for a job report.
    Classes
  • Robert O'Connor_4
    Robert O'Connor_4 Member Posts: 88