comparison of hoffman 75's to gorton
john_27
Member Posts: 195
I have a 2 pipe steam system which uses a hoffman 4a and a Hoffman wr as main relief valves.The system takes 25 minutes to fill the mains which are each 6 inch by 110 feet. After reading Dan's comments in his book, and after visiting Hoffman's web site, I removed both valves, and steam came out of the relief valves 8 inches after ten minutes. I am thinking of Hoffman 75's, but
Gorton also makes a #1 and a #2 valve. The system is a Broomell with the condensing radiator still in place but disconnected from the system and the chimney. The sytem runs on 4-8 ozs. of pressure. One unfortunate fact...the relief valves: 1. Have a thin coating of oil on them(possibly because I just unclogged a wet return which had been clogged for many years, and 2. The placement on the main return is only 6 inches from the end of the return. Also, no vents at the end of the two supply mains, but this is a two pipe instead of a one pipe system. Would anyone have thoughts on the best valve,number of valves needed, and whether the oil is from the fixed return or the boiler needs cleaning somehow.
Gorton #2 is the best for that system
and if you have two 6-inch, 110-feet-long steam mains it must be a pretty big system!
In order to vent each of these mains properly, use four Gorton #2 vents after the last radiator takeoff from each main. Vent the dry returns with at least two Gorton #2 vents- or reconnect the condensing radiator and chimney vent line.
www.gorton-valves.com
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Consulting0
- 86.8K THE MAIN WALL
- 109 Chimneys & Flues
- 5.6K Gas Heating
- 966 Plumbing
- 385 Solar
- 15.3K Strictly Steam