Steam boiler
Installed a steam boiler, installed all new near boiler piping. Everything done per. mauns specs. I noticed that the boiler water level will disappear after 5 minutes the unit will go off on low water the feeder will not feed any water (set for 2 min delay) into the boiler and a few seconds later the level will rise up to 1/2 of the gage glass. I flushed the boiler my question is where is the water going. The unit runs great there is no water hammer. So I think the water is returning to the boiler. I think i should go back and re flush the boiler. can someone explain to my by having oils in the boiler how does that effect the steam and causing the surging
Al
  • With oil in the boiler
    it forms a slick on the top of the water , and when the boiler starts steaming it has to break through that slick - which will send plumes of water up with the steam . Not the best way to produce nice dry steam into the system .
    The water , or condensate , takes time to get back to the boiler . Depending on the size of the radiation , if the pipes are insulated , the size of the return pipes , or how restricted they are , the boiler can go off on low water quite a bit . That built in delay is a very nice feature to make sure the boiler does not over fill .
    How big was the old boiler you replaced ?