Tom_9
Member Posts: 1
I have Weil McLain 368st steam boiler,oil fired.one pipe system.With two 2 in mains,one is 18 ft long,the other is 12 ft long.On the 18 ft main i have two #1 gorton valves, on the 12 ft main i have one # 1 gorton valve on it are these valves big enough. thank you Tom
0
Comments
-
Gorton says
the #1 vent will vent 20 feet of steam main in a house.
No mention was made of size of main but 2" is about a small as they get.
Regards,
Robert0 -
Those Gortons
should work fine!
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Steamhead
I took your advice and ordered a few #2 vents from them. Nice people to talk with and the products look good.
They were delivered to me in Maine the next day!
In the past I had doubled up Hoffman's to get capacity but these have more capacity and less money. They are , as you know servicable I am told. It seeems odd that no one else offers a vent in this size for the residential light commercial market.
All the best,
Robert0 -
Now you know
why I like their gear so much! And I'll bet the system you used them on worked a whole lot better.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 167 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements