On a Vitogas 100
Steve Ebels
Member Posts: 904
Operating with a 200 series control, what has to be hooked up in order for the cycle counter and burner hourmeter to function. I don't see what I missed but they are not clocking anything.
Vitogas
Steve,
Burner feed back only works on the burners with 120 volt circuits such as the Vitola and Vitorond. There is no feedback from the Vitogas 100 or 50 because the ignition is only 24 volts therefore the hour counter and fuel usage can't be calculated.
kf0 -
I wondered
If something like that was the case. Buderus is the same way. If you want it to count you have to install a 24V/110V relay and wire it to the burner terminal. Could probably do the same with the Viessmann if you knew which terminal to wire to on the control.0
- 167 Indoor-Air Quality