Panel Radiator
Options
George Haselton
Member Posts: 2
We retrofitted a geothermal heat source into an existing house. Many of the existing floor areas had polybutylene tubing in the slab for the radiant heat. In any new areas, we used a barrier pex. One small area had a concrete floor and no tubing. We installed a steel panel radiator by Buderus. In about a years time it sprung a leak. Apparent cause was corrosion. conclusion is the polybutylene tubing must be letting Oxygen in. The entire system is either pex or non-ferris metal like copper. Assuming this was not just a bad radiator, but really was affected by the lack of barrier, I need to find out if there are any panel radiators made out of non ferris metal? Can anybody help?
George
George
0
Comments
-
PB
Rather than look for radiators that can tolerate oxygen, why not separate the PB system from the PEX/radiator system with a heat exchanger (HX). That way, any oxygen that enters the system will be separated from non-ferrous components.
The PB side of the HX will need its own fill valve, circulator, air eliminator and expansion tank; all non-ferrous of course.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0
This discussion has been closed.
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 167 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements