sizing steam pipe
I forgot to ask, how large are the 3 radiators you installed new to this system? (Each on a 1" riser)
  • Mark_11
    Mark_11 Member Posts: 4
    I recently had a 2nd story addition (2 bedrooms and a bath)put on my home. The 2nd floor doesn't get as warm as 1st. I have one pipe steam system. The plumber put 3 new radiators in, however I'm not so sure of his piping method. Out of a 1" tee in the main, he ran 1" copper then tee'd to 3-1" uninsulated risers to 2nd floor. Could this posibly have the volume needed for 3 radiators in a 420 sq. ft. addition?
    Anyhelp would be appreciated. Thanks
  • A 1\" undripped
    riser is rated for 45 sq. ft (10,800 btus).
    If I understand you, there are 3 - 1" risers off of 1 - 1" connection to the main. If that 1st piece of 1" is horizontal, the numbers change to 28 sq. ft. (6,700 btus)available to feed 3 - 1" risers.
  • Mark_11
    Thanks for responding Ron. Yes the first piece of 1" is horizontal for about one foot to first tee, then horizontal another 12 feet to second tee, then horizontal another 10 feet to last verticle riser. I don't know how much radiation I have or how much I need but 28 sq.ft doesn't sound like much.
  • Mark_11
    waiting
    for wetheads to return.
  • George Berkeley
    George Berkeley Member Posts: 40
    Pipe size
    The numbers read that with this system that 2nd floor will always be under heated. You are volume starved at the header. Let alone the impact at the boiler size.
    Steamhead Member Posts: 18,205
    Branch steam line
    I'd go with a 2-inch black steel pipe to supply those 1-inch risers. Also provide a place to install a vent at the end of the new 2-inch pipe. Vent the pipe with a Gorton #1 or Hoffman #75.
    Copper on steam lines is always a bad idea.
    Consulting
  • Mark_11
    i'm not sure
    how radiators are measured, however 2 are brand new 'modern types' 1 is 4 section the other 12 sections, the 3rd radiator is a very old one about 7" deep, 27" high about 12 sections