No PEX within 12\" of recessed lighting?

Paul E.
Paul E. Member Posts: 7
Why is it that they say not to install PEX within 12" of recessed lighting? Is it because the lighting might heat/melt the PEX? Or is it a UV thing (light escaping from the can might hurt the PEX?)

On a planned underfloor staple up job, in the basement I have IC rated recessed cans for lighting. Above the cans would be a layer of insulation, then the aluminum plates, then the PEX. I can touch my hand on top of the recessed can without pain <g> - it doesn't seem like the light can is gonna hurt tubing with 130 degree water running through it???

Thanks,
Paul

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,632
    Who

    says this?
    Retired and loving it.
  • bruce pirger
    bruce pirger Member Posts: 111


    I believe it is in the Wirsbo design manual...I have read it as well.

    I don't know, but I assume it is fear of heat and a tube actually touching a can and eventually melting.

    That's my guess and assumption.

    If its burried behind insulation...I can't believe its a problem at all. I have it over my cans anyways.
  • Don Robertson
    Don Robertson Member Posts: 43
    sounds familiar

    I recall hearing the same thing. I believe I heard it at Wirsbo factory training. It may have more to do with the high temp affecting the lighting. I'm not sure but I will check my notes and get back to you if I find anything.
  • KCA_2
    KCA_2 Member Posts: 308
    I believe

    It's because of the heat potential. All pex, that we've used, has the same standard as well it's a part of our local code.

    :-) Kca
    :-) Ken
  • Terry
    Terry Member Posts: 186
    safety first?

    would it have something to do wiuth putting waterline over electrical device?

    same reason you do not run your waterlines over your breaker box.

    Terry
  • Paul E.
    Paul E. Member Posts: 7
    Here's the links to RTI's manual -

    For the plumbing pex, top of page 6 they say 12" vertical and 6" horizontal clearance with a little drawing:

    http://www.radiant-tech.com/assets/documents/PlumbingDesignInstall.pdf

    For the heat pex, just one line at the bottom of page 6. No explanation why in either case.

    http://www.radiant-tech.com/assets/documents/HeatingDesignInstall.pdf

    -- Paul
  • hot_rod
    hot_rod Member Posts: 24,860
    The newer style

    can lights are a double wall product with thermal cut out switches. I have noticed these IC's run much cooler than the old style cans.

    If you "over bulb" them they trip the thermal cut outs. Hard to believe you coulcdn't pex within a foot of those, especially with insulation between!

    hot rod
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Rene
    Rene Member Posts: 7
    bonded

    What do you think about bonded pex-pipe with an aluminium coated surface inside. No fear of heat.
    Ciao Rene
  • KCA_2
    KCA_2 Member Posts: 308
    The aluminum

    would do fine, it's the PEX that still has an issue with the heat..

    :-) Kca
    :-) Ken