Steam Actuators with end switch ?
John G. Merritt
Member Posts: 140
Fellas:
I have a steam Actuator (5 wire) that I am told needs an end switch in order to start the Oil Burner as the Valve opens. I'm not sure how to wire this, as I have never done it. There is RWB to motor and TT for Transformer.
Can anybody draw me a schematic on how to add and wire in this end switch? There are 3 others (3wire) which bring on the burner as the valves open. Confused. Somebody added this 5 wire & it doesn't work.
John
John
steam accuater
who is the manufacterer and what model no. is it a honeywell zone valve?
control
john,
is this a multi zone steam system, depending on your control ideas what generaly happens is that the end switch enables the boiler control any zone can do it but if none need it you don't maintain any steam pressure if you have a tankless it is wired in the same circuit that way all the saftey's are invoved and its not hard to find the open when there's a problem more specs would help
chris smith
paradise porter maine
ps have a merry whatever your faith or inclination0 -
Actuaters are Honeywells
Fellas,
These actuators (3-3wire) and 1-5 wire are Honeywells.
The one in question, a 5 wire, is a #ML6984.
How do I wire in an end switch so that valve operates the burner? The other 3 operate the burner when they open.
I hope this info helps.
John0 -
TT
usually indicates a switch of some sort.
Are these new units you are installing?
Mark H
Mark,
Only the 5 wire valve is newly installed;
John0 -
I'm still
looking up that model actuator,but I would think that the TT is your end switch.
You would wire it in as you would a themostat to the burner circuit at the boiler.
Just a guess at this point, but I am looking it up.
Mark H
hey guys i dont think john merritt is real ive tryed to send him an e-mail it comes back as unknown
I'm real enough.
Hey Ed,
I'm real. Ask Dan.
John0 -
Try this
http://hbctechlit.honeywell.com/techlit/PDF/95c-00000s/95C-10879.pdf
I was wrong. T5 & T6 need to be powered from transformer.
Mark H
steam zone valves
i did one last year in cambridge ma if you are in eastern ma. i can show you what i did
Thanks Mark
Mark,
Thanks for trying to help. I have to get more info.
And Mark, I'm real.
John0 -
I know
I've seen you here before!
Sorry I couldn't be more help.
Good luck!
Mark H
John's
real.Retired and loving it.0 -
johns real
sorry dan i didnot know it was possible to have an unlisted e-mail address i thought that the e-mail address that showed up with a posting would be the address to reach somebody instead he has a differant address
E-mail problem here
When I click on the somebodys address on the Wall posting, the E-Mail goes through!!
If I type it in on "New Mail" they all come back UNKNOWN!
Can anybody explain this to me. Perplexed.
Thanks,
John0 -
I feel for ya....had the same problem last year...there's one ma
who can definitely get you through it: Noel from Slant Fin. He got me through that nightmare. Mad Dog
Need help with nightmare
Hey Maddog!
Need help with the nightmare! How do I reach Noel from Slantfin??
John0 -
Thanks Ed Wallace
Thanks Ed for faxing the schematic. Solves the problem!
John0 -