converting inches water column to psi
smoore
Member Posts: 28
When dealing with gas preasures how do you convert inches water column to psi?
16 inches to the LB
2000 International fuel gas code book....
> _A
> HREF="http://www.heatinghelp.com/getListed.cfm?id=
> 169&Step=30"_To Learn More About This Contractor,
> Contractor"_/A_
page 106.....
27.7 in. H2O = 1 psi.0 -
Roughly 28\"= 1 PSI
Best I can come up with is a mult. to convert 1 foot of water to psi. Feet of water x 0.4335= PSI. I divided .4335 by 12 (in per ft) for a mult. of .036125. So, inches of water x 0.03625 = PSI. 1 (PSI)/0.036125=27.682...roughly 28".
Larry0 -
Hmmm....When in Rome
I've always used 27.8. Have read 28.8.
Guess it depends whether the code author resided in a costal place (sea level) or a mountainous place?
Just like it affects those darn gas orifices. Oh I have a story to tell over a campfire and some libations about a boiler company in Ohio and a delivery in Alberta Canada. ;-)
I live at 3500' above sea level.0 -
Temp is a factor
Temperature is a factor depending upon precision needed:
1 lbf/square inch (PSI) = 27.707591 inch H2O (60 F)
1 lbf/square inch (PSI) = 27.680671 inch H2O (39.2 F)
Also, molarity:
1 foot H2O (39.2 F) = 0.974191 foot seawater
See http://www.onlineconversion.com/pressure.htm0 -
Don't listen to Larry - I think he's thinkin' ounces. (Sorry, Larry....)0 -
To coreysnow from joe
Your equation of 0.974191 ft/seawater only holds true for measurements taken from the North Atlantic or Adriatic Sea. You would have to make a correction factor for readings taken from the Great Salt Lake, the Dead Sea, or the Caspian Sea. The converse holds true for the brackish waters that contain less salt than the aforementioned. Pi-delta-t has to be factored into it. Or square the difference between the densities. Hopes this helps!0 -
one pound of pressure will raise a column of water 27.7 inches high. We measure most residential and light commercial gas sysems in water column. Most LP systems operate at 11" wc. Most natural gas sysems work at 3.5 " wc.
Dave Flood
Director of Tech Ed
ICPA
Wallingford, Ct0