Looking for Combination In-Door Pool
Chris Maderia
Member Posts: 120
dehumidifier and heat source. I am in the process of designing and quoting a job and am in need for info on the subject unit. The pool itself is 16x32 (15,000 gals) and will be covered when not in use. I am using a pool heat exchanger to heat the pool and also doing radiant in the slab. The radiant will be to only condition the slab. I am figuring 20btu's per sqft which turns out to be 20,460btu's. I figure on running 4 loops of 1/2" pex 12" OC with each loop being 275ft. My flowrate is 2.73gpm @ 8.10ft head. I also figured on using a Tekmar 150 Set Point Control Just for the slab. If anyone has any suggestions and can recommend the subject appliance please let me know. Thanks.
pool dehumidification
the last one we did we used a boss aire double pass air to air with a hot water coil to keep the air temp up. that's really the key. tempering the slab is good but to keep the humidity down it is necessary to keep the actual air temp in the room 3 degrees warmer than the water temp, and it also helps to keep it covered when not in use. you can find boss aire at www.bossaire.com
good luck, Paul0