Gas Pipe sizing tables
does anyone have tables for low pressure gas pipe capacity in BIG sizes?
I'm looking for under half pound 6" at a 300' length.
Thanks, Noel
  • Floyd
    Floyd Member Posts: 429
    International Fuel Gas Code
    2000 page 32 Table 402.3(5)
    Press. under 1 pound .3" drop
    6" 300" says 8,145
    Hope this is what you were looking for.
    Floyd
  • perfect.
    Can you fax me that table, just that one? I'm at 516 484 6958
    Noel
  • Floyd
    Yup
    Give me a couple or 3 minutes, I have to scan it first.
  • Floyd
    Noel
    You should have it now
  • thank you
    just the thing I was looking for
    Noel