R-value of air space. - Alan(CaliforniaRadiant)Forbes
Member Posts: 1,243
This has probably been discussed before, but I can't remember the outcome.
One of our contractors is building a room that will be a dance floor; it has to be springy like some basketball courts I've seen. The floor construction will be: concrete slab-flat 2x4 sleepers-hardwood. This means that there will be 1-1/2" of air between the hardwood and the concrete.
I need an R-value for that space so I can plug it into my heat calc's. Any ideas.
Alan
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=53&Step=30">To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"</A>
Alan
Hard to find and inexact
r-value of 1/2" - 4" of air: APPROX 1.0
BUT, I don't believe this is "all of the story." You also need to add "air film" resistance values for both the top of the subfloor and underneath of the finish floor. Approx r .6 each? Total now about r-2.2. Since 1 1/2" softwood has 1.88 you should be safe using the r 2.2 number.
http://coloradoenergy.org/procorner/stuff/r-values.htm0 -
r value for air space
straight out of ASHRAE..let me know if you can read off the 1.5" column....if not, i'll e mail you a .pdf...i'd say it's approx 0.80
- 87K THE MAIN WALL
- 112 Chimneys & Flues
- 106 Geothermal
- 979 Plumbing
- 388 Solar
