I have a steam boiler that recently stopped refilling with water. I hired a company that advertises steam boiler service, and they replaced the low-water cutoff (LWCO). The boiler ran fine for two days, then started building pressure and making a loud noise like an air compressor venting pressure.
The company came back and replaced the pressure controller, but the problem is still happening.
I’ve lived in my house for 5 years and have never heard this sound come from my boiler. After spending over $4,000 on repairs so far, I’m now dealing with an issue that seems serious and could potentially damage the system.
What could cause a steam boiler to build pressure and vent loudly like this after an LWCO replacement, and what should I check or ask the tech to look at next?
Here is a link to a video of the noise,however, the boiler has made much louder and rapid noises
Where is the pressure gauge ??? Does it work ?
When they replaced the Pressuretrol did they verify the pigtail and the whole path between the Pressuretrol and the inside of the boiler is not blocked ? Is the Pressuretrol set to the minimum ?
I would think the pressure relief valve is relieving pressure.
One Pipe System0 -
That Foghorn sounds like the MM 47-2. I'd like to see pictures of all sides of that boiler and piping. Mad Dog
I agree. I have had that on a few jobs in the past and have added a 1156 before the 47–2 and that solved it.
Yes…that’s what it is.
Is the water level bouncing in the sight glass as this happens?
The LWCO float may be bouncing also, shutting down the burner and then adding some water giving you the foghorn sound.
Just a WAG.