Issue with gas fireplace

Options
zepfan
zepfan Posts: 498

the below picture is from a Peterson fireplace with a standing pilot, thermocouple. The pilot is lit, but the only way the main burner will light is if the knob on the right is turned to on. It will not work from the customer’s remote. The insert is 20 years old, and both the receiver and remote were replaced two years ago. The batteries are new in both. I tried the re learn sequence with the remote, but still no action from the fireplace. I am getting an audible beep out of the remote, but still nothing from the fireplace. I can remove the two wires that run from the transmitter to the valve, and when the remote is placed in the on position, I have continuity between the two wires. Same holds true when the transmitter is in the remote position, and the on button is pressed on the remote, I have continuity between the wires on the valve. If I remember correctly when the fireplace is working the knob on the right should move automatically when the remote is pressed on. I am assuming the motor in the valve is bad, that is the reason it is not working with the remote, but I never had one of these go bad, but this is a 20 year old unit that the customer uses a lot. Any suggestions would be much appreciated. Thanks to all

IMG_7067.jpeg

Comments

  • mattmia2
    mattmia2 Posts: 18,513

    does it have power? does it turn on if you short the t-stat wires? the safety valve likely runs off the thermocouple so it doesn't need power to keep the pilot lit.

  • EdTheHeaterMan
    EdTheHeaterMan Posts: 13,067
    edited 3:40AM

    As I understand this model, you light the pilot and turn the dial on the right to ON. The remote control sends a signal that operates a motor, which turns the dial on the left.

    That dial provides gradual flame adjustment, starting at OFF at one end. As the dial rotates counterclockwise, the amount of gas increases gradually until it is fully open, producing the largest flame. You can adjust the flame size and stop the motor at any point in its rotation to achieve the desired flame height.

    If the valve motor is no longer operating, then you will need a replacement gas valve equipped with that same motor.

    This might be the part number you need. SV-22 for natural gas or SV-23 for propane https://www.realfyrestore.com/real-fyre-control-valve-body-for-apk-15-valves-only-natural-sv-22?utm_source=chatgpt.com

    EDIT: A new complete log set might be an easier fix and less expensive after your professional fireplace repair tech charges a mark-up on the part and the necessary labor to make the repair.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    zepfan
  • Bob Harper
    Bob Harper Posts: 1,194

    You can connect 6 vdc to the two polarized spade terminals. One orientation should cause the servo to open then reverse to close. If it does not rotate freely and operate the valve, the valve is shot. On a logset that old, we recommend full replacement with new style logs and burner with an Intermittent Pilot Ignition system and listed to ANSI Z21.60a. Someone may have tried to use line voltage on that Maxitrol valve and fried it.

    EdTheHeaterMan
  • zepfan
    zepfan Posts: 498

    Thanks for the responses. The valve just has a thermocouple, and jumping the two wires connected to the receiver results in no response from the valve. I have to believe that after twenty the valve has failed, I don't know what else it could be. No one tried to connected a line voltage to the unit. Although I did not install the insert initially, I am the only one that has serviced it annually for the customer since 2009.

  • EdTheHeaterMan
    EdTheHeaterMan Posts: 13,067

    Thanks for the responses. The valve just has a thermocouple, and jumping the two wires connected to the receiver results in no response from the valve. I have to believe that after twenty the valve has failed, I don't know what else it could be. No one tried to connected a line voltage to the unit. Although I did not install the insert initially, I am the only one that has serviced it annually for the customer since 2009.

    I don't think that jumping will do what you want. You may need to apply voltage as @Bob Harper mentioned. but I could be wrong. I would need to see the actual valve and the wiring with the new batteries you installed. Four AA batteries will provide 6 volts DC or you might be able to get 12 volts DC from your model train power pack. Perhaps that can do what you need with the variable speed adjustment on the power pack at half speed.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    mattmia2zepfan
  • mattmia2
    mattmia2 Posts: 18,513

    going on what @Bob Harper said, check the input to the motor with a voltmeter when trying to turn it up or down. if you see voltage it is the valve, no voltage it is the control or its power supply.

  • 109A_5
    109A_5 Posts: 4,841
    edited 6:39AM

    You are not trying to operate it in pilot mode are you ?

    image.png

    " I can remove the two wires that run from the transmitter to the valve, and when the remote is placed in the on position, I have continuity between the two wires. Same holds true when the transmitter is in the remote position, and the on button is pressed on the remote, I have continuity between the wires on the valve. "

    The Transmitter has no wires.

    The box with the 6 Volts worth of batteries and with the wires is the Remote Receiver. To command the Gas valve the 6 Volts is sent through the wires to the gas valve. I would not expect continuity looking toward the Remote Receiver. I would expect 6 Volts that the polarity reverses depending on the command sent to the gas valve.

    I would expect continuity measuring the terminals on the gas valve, that would be the motor.

    image.png

    image.png

    Troubleshooting info. in the document.

    https://www.rhpeterson.com/login/realfyreinstructions/A2-283.pdf

    https://www.fireplacedoorsonline.com/images/companies/1/Images/RealFyre/Controls/RR-1A-Manual.pdf

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • zepfan
    zepfan Posts: 498

    thanks for the responses. no the picture was taken in the pilot mode. obviously the it was switched to the normal position of on