The B & G 109024 operators have been discontinued and I wondering if they are perhaps still on a supply house shelf somewhere and I need to re-stock. I'd even buy the 109017 valve complete. Once I run out of the operators, I'm looking at having to replace the entire valve. Does anyone have a source?

mail.google-2.jpg
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

Two btu per sq ft for degree difference for a slab

Comments

  • hot_rod
    hot_rod Posts: 28,846

    the common failure is the heat motor, but why buy one at this $$?
    do you prefer thermal electric valves?

    IMG_1821.jpeg
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • mattmia2
    mattmia2 Posts: 18,507
    edited 12:10AM

    why would someone buy $1k for a zone valve actuator? Are they for like 6" pipe or have a super high Cv?

    (maybe the price i saw was gouging because they are discontinued)

  • Thermal electric valves are not a preference, but an easy operator change-out is.

    I've still got a bunch of Honeywell motors for the Honeywell V8043 zone valves, but have lost the inclination to replace them. So, changing the heat motor in a B&G zone valve doesn't interest me.

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • mattmia2
    mattmia2 Posts: 18,507

    changing the operator in a taco zone sentry is even easier. the wiring connections are phoenix connectors so they just unplug and plug in to the new operator

    Alan (California Radiant) Forbes
  • Steve214
    Steve214 Posts: 29

    Maybe Sid Harvey’s has some laying around??

  • EdTheHeaterMan
    EdTheHeaterMan Posts: 13,057

    An opportunity to make some money here. Or are we no longer interested in selling new products when the old ones become obsolete and are no longer available?

    If that were the case, we would all still be servicing coal conversions installed in the 1930s and retrofitted with automatic burners in the 1950s. Nobody would ever need a new boiler except builders of new homes.

    This reminds me of the excuse some contractors use to avoid testing pressure relief valves. The green, white, or yellow tag attached to the valve's test lever instructs the owner or technician to "operate" the valve annually. The thinking seems to be, "If I operate the valve and it starts leaking afterward, I'll have to replace it."

    Isn't that exactly what we're in business for? Replacing defective components and making sure the system is safe to operate?

    It's all in how you present the solution to the problem. I made plenty of money keeping a selection of pressure relief valves in stock on my service vans.

    You might consider having a flat-rate price ready for replacing older Bell & Gossett (B&G) valves with a replacement valve of your choice. Offer the customer the option of having it replaced now at a discount price or scheduling the replacement later at your regular service rate. (or the other way around, whatever suites your service schedule that day).

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • GGross
    GGross Posts: 2,123

    I can check with the rep in michigan. the last time I sold one of these was in 2014! not too common around here.