bullhead

Options

system near piping specs: 8 radiators, two pipe, steam main is closed loop, radiators do not have pea traps, special elbows on return, or orifices. the control input valve is 0-10 . Vaporstat control in ounces. Bog mouth vent on dry return. line in basement.

Issue: short cycling, uneven radiator heat output. Attempts to resolve the problem - different valves - Hoffman, rainmaker, big mouth.. Vaporstat adjustments, radiator throttling.

Boiler was not installed to installation manual. - Installer and Utica technical department said that the bullhead take off to steam main is ok.

√

8DE8AB85-095F-496D-B846-3ABE1CC91FD5_1_105_c.jpeg

stean main closed loop.png

3A918B73-2611-44C1-865F-63DD75CE52BA_1_105_c.jpeg

IInstaller and Utica technical department says that this is ok.

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,398

    We see a lot of boilers pipe wrong, but they work. Not optimal but if it works it works.

    The more important thing is how does it run????

  • KC_Jones
    KC_Jones Posts: 5,966

    Just to clarify. Are you saying the main runs out and is capped on the end? I ask because there are signs at the boiler this is a counterflow main. Those tee's at the boiler facing down would normally be for drips on the main to allow the condensate to return without impacting the steam flow from the boiler.

    The bullhead tee might not be the primary problem, but it's still not the way to do it with a newer boiler. That said if the manufacturer is contradicting their own manual, I don't see you getting much support to fix that unless you want to pay the contractor again to pipe it.

    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15