Vents on bottom of hydronic return

Options

II have seen this yet. These manual vents are located in the basement near the boiler on baseboard return lines from 2 upper floors. Does this work? Does it seem like it would to me.

5265.jpg

Comments

  • leonz
    leonz Posts: 1,997
    edited 4:51PM

    🤬two more places for leaks, and just lazy in my opinion. It is simpler and less messy to simply turn the heat all the way up for a couple of hours to push the air bubbles out of the system.

    4 short nipples, ball valves and two pipe caps would be safer and less likely to cause burns.

    My thought anyway.

  • Operadox
    Operadox Posts: 2

    From your photo those look like they sit at the bottom of the drops, pointing down. A manual vent only lets out air that collects where it is, and air goes to the high points, so down there it won't vent much. Open one and you'll most likely just get water. They could still be handy as drain points if you ever need to drain those loops.

    The air on those two floors has to come out at the high points, usually vents at the ends of the baseboards upstairs, or by purging the loops from the boiler. Do the baseboards up there have vents on them?

  • HydronicMike
    HydronicMike Posts: 486

    Might have been put in for convenience on initial fill up. Could've also been used if they have monoflow tees, but it doesn't look like it.
    Either way I wouldn't touch them unless you plan on cutting them out and replacing them.

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,398

    just look at where they are installed. They are drains at the low point. This is very common. What does a coin vent and a baseboard tee cost compared to a 1/2" boiler drain and a copper tee?