Using a perimeter induction coil in residential.

Options
Kaos
Kaos Posts: 1,009

Going down a bit of a deep rabbit hole trying in hopes of making some version of hydronic cooling work in residential.

One idea is to use something like this with a bit oversized ERV supply.

https://ebaircontrol.com/wp-content/uploads/2025/06/induction.pdf

These use an extarnal air source through a venturi plate to pull air through a hydronic coil. Gets way more output out of the same size coil over regular convectors.

The idea is that one already needs to duct ERV to rooms, why not also use it to help drive extra airflow? Some of the units also come with drain pans so it could also do cooling. Rough math says 1/2 ton out of a 3' unit.

This means no fans inside coils, no extra wiring, exiting zone control valve for both cooling/heat.

Anybody see anything like that out in the wild?

Comments

  • hot_rod
    hot_rod Posts: 28,807

    good to see you are still on the search. New to me that induction principle. Although after snooping around it looks like Carrier used this technology years ago.

    Have you chatted with that manufacturer?

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • mattmia2
    mattmia2 Posts: 18,476

    i think my elementary school from the 50's was built like that, it had tunnels under the floor that they ducted air in that was pushed up through the convectors around the perimeter. also everything was made of asbestos

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,393

    I remember something about induction units. Never saw one. I think some of my old books' Carrier manual and 1964 Ashrae book may have something.