Hi All,
I have an old tall steam radiator located in a room in such a way that it blocks a larger bed from being placed against the wall. (see attached pictures)
I realize, if I use a lower profile baseboard radiator. I can move the radiator to the adjacent outside wall, underneath the window. Freeing up the entire back wall for the head of a bed.
The ceiling underneath the room is open, so I might be able to move the pipe, or I could extend the pipe above the floor and make sure it is pitched properly so it drains. It is a single pipe steam boiler system.
Does doing this substitution work? Are there any gotchas I should be aware of?
Comments
-
Those baseboards only output 3.4 EDR of heat per 1ft. So this baseboard is only like 14 EDR… As much output as, like, 1/3 of that cast iron radiator…
»»» See my steam heat YouTube videos:
https://www.youtube.com/@HeatingBlog2 -
you could put a short radiator or convector cabinet under that window.
the mass of that baseboard is a lot less than of a standing cast iron radiator of equal edr so the baseboard will heat and cool faster than the rest of the system so the heat will have spikes of too hot and too cold(or to cold and even colder if you don't match the edr to your current radiator)
baseboard can be difficult to get condensate to drain from on 1 pipe steam. With that short section it isn't that bad but longer sections do better set up with a condensate return at the end opposite the steam supply end. There are several ways to do that on a 1 pipe system.
2 -
-
-
Okay, good to know. I do that with hydronic heat when space is at an absolute premium. It does take awhile for them to heat up.
0 -
Try to find another cast-iron radiator that will go under the window. Match its capacity to the existing rad.
If you post an end view of the current rad, and give us its height (which I think might be 38 inches) we can tell you what you need.
2
Categories
- All Categories
- 87.9K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 430 Carbon Monoxide Awareness
- 134 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 80 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 397 Solar
- 16.1K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements