Expansion Tank Location on Viessmann Boiler Installations

Options
Alan (California Radiant) Forbes
edited November 1 in THE MAIN WALL

I was having problems with the diverting valve on a new Viessmann Vitodens 100-W (B1HE-150) boiler. It would freeze in the heating position and the boiler would stop making DHW. I would get the call and would have to exercise the diverting valve, either in the service program or by hand. Speaking with technical support, he asked me if the x-tank was on the supply or return. Mine was on the return and he told me that when the tank is on the supply side, a vacuum can form because the diverter is also on the supply side and can cut off the function of the x-tank. Kinda' makes sense, kinda' doesn't. Nevertheless, something to keep in mind during installation.

0.png
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

Two btu per sq ft for degree difference for a slab
0.png 81.9K
GGross

Comments

  • kcopp
    kcopp Posts: 4,744

    Any water quality issues?

    I had diverter issues on a few Weil CGt units and there was poly B in the system.

  • GGross
    GGross Posts: 2,123

    I have heard of some vacuum issues but not sure if the tank would really be the cause. I have most of the local contractors on board putting the xtank on the return, I'll make a note the next time i get a call about it maybe all of them have goofy tank locations. typically I assume the majority are just a little stuck like what you are seeing, maybe some little scale or air gets trapped. I try to get techs to just manually move it but they just want to change parts so it almost always gets changed lol. They did make a check valve with a vacuum relief specific for the B1KE199 so i know there was some issue they found out in the field with that one specifically.

  • So, even with the x-tank on the return, the diverting valve kept sticking. Last Friday, I replaced the diverting valve and this morning, I received a text from the owner that it is stuck again - no DHW. He's a pro now and knows how to exercise the valve with the actuator test. I seem to remember a check valve on the DHW piping and Viessmann wants me to remove it. They also want me to remove the diverter valve and operate it in vitro as, for some reason, this seems to cure the problem.

    @kcopp The water quality is good. Barrier PEX.

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • GGross
    GGross Posts: 2,123

    I had trouble with one when these first came out it wouldn't move but we could pop off the actuator and move it by hand. We ended up finding a check valve where there should not be a check valve, when it was removed everything worked as expected. Sorry i can no remember the specifics, but the check valve was in the DHW side piping on a unit heating an indirect, not a combi

    Alan (California Radiant) Forbesbjohnhy
  • 8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
    SuperTechGGrossPC7060
  • Removing the check valve did the trick. The diverter valve in the boiler has been working fine since.

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
    PC7060GGrossbjohnhy