Vtx hydrolevel
have a Burnham IN7 steam boiler with a 24-volt control system and the factory-installed McDonnell & Miller 801-120 low-water cutoff. I’m installing a Hydrolevel VXT automatic water feeder. The VXT has power, but I need to know exactly which terminal on the factory 801-120 should provide the signal to the VXT FEED terminal when the boiler is in a low-water condition.
My 801-120 has only one C terminal. Which terminal/wire should I use to trigger the VXT feeder? Could you please provide the correct wiring diagram for this setup?
Comments
-
I sent to Macdonald miller via the text help
0 -
Looks like terminal 4 calls the feeder. Here is the diagram from a M&M Uni-Match feeder that shows the PS-801-120:
https://controlssupplychain.com/wp-content/uploads/manuals_pdf/mcdonnel-miller/CSC-mm-Uni-Match.pdfCo-Founder, All Steamed Up, Inc.
Baltimore, MD, USA
0 -