Suck start my boiler
Last year, during a period of very high dew points, my HTP UFT 80 boiler tripped out on flame failure. It heats my domestic through an indirect tank, but it hadn't been used for a full day. Thus, everything was basement temperature: still quite cold (Wisconsin). I opened up the top of the combustion chamber to find the burner saturated with water. I determined that this likely came from outdoors and just kept condensing on the burner surface so the gas/air could not ignite/get sensed properly. I shook out the water, re-assembled, and it took right off. Fast forward to this week, when dew points were in the mid 70s and the basement is still cold as it is only June. 9:00 at night; I want a (warm) shower and bed…. The light bulb in my head went on and out came the shop vacuum. I went to my boiler exhaust outdoors and put the vacuum up to it for about 20 seconds and pulled some water droplets up and out. I went down to make sure the condensate trap still had the proper level in it, reset the boiler, and it took right off. Of course, as a retired HVAC Service person, I triple checked all my venting, drains, etc. This is just a quirk that I have now have a quick fix for…
Jay W.
  • GroundUp
    GroundUp Posts: 2,571
    That's not a fix. There should never be water in the burner, ever, for any reason. Either the HX is leaking and spraying the burner, or the HX is plugged up so badly that the condensate can't drain (very common with the UFT's Kiturami HX running low temp radiant); maybe even both.
    Grallert
  • JayWisth
    JayWisth Posts: 4
    Nope. There should not be. The boiler gets a good clean and check every year. Indeed, the fire side is an absolute bear to clean, but I make sure it is very clear. I bought this boiler as a quick replacement - the piping lined up very nicely with my old boiler in 2020 (availability???). There are likely better choices out there if I do more research and have the luxury of time to allow for piping changes. It is five and a half years old. The water sits up on the stainless perforated plate (it's horizontal) and gets stuck in that material between, effectively blocking most of the flow; allowing some as I can smell the raw gas outside on ignition attempts. It's just the gas/air mix is either way off and/or getting through nowhere near the ignitor due to the restriction. I reported this to the local HTP representative's service technician last year for his information and possible input.
    The inlet and outlet vent piping is quite short and an appliance temperature 20 degrees below the dew point outside is my strong suspicion. The exchanger itself is dry, so I believe the moist air drifting in is mostly from the inlet piping, through the combustion blower and onto the burner surface.
    I do run quite low temperature radiant and stay in condensing range for my domestic as there is only two people in the house and don't see the need to go super hot for that. This has only occurred during these high dew points, not in heating season. It recovers plenty fast and I have enough mass in the floor that I never notice any drop in floor temperature during domestic production in winter.
    I do appreciate the input and will be that much more attentive during the next cleaning or sooner if this is a repeat occurrence before then.
    Jay W.
  • GGross
    GGross Posts: 2,072
    edited June 12
    thats not a quirk. those units are made to drain condensate, if its not draining condensate you need to service it, if its leaking from the water side to fire side its shot. you should be able to take a hose to the fire side after cleaning and it should drain free and clear out the condensate drain, if it starts backing up then its not yet clean,
    mattmia2 Posts: 18,233
    isn't there a flap that would more or less prevent gravity air flow through it?
  • JayWisth
    JayWisth Posts: 4
    I have ruled out a leaking heat exchanger. Feed water has been shut off since last service, September, which it gets every year at that time, by me. Only then to check compression tank precharge pressure and refill. Agreed, condensate back-up would be an obvious issue, but trap and exchanger was draining properly before and after. Condensate is ordinarily produced during combustion and flows downward, through the fire tube heat exchanger. This is a whole different scenario, where water is stuck where the engineers never thought it would produce condensate or take in water. This is clearly outside the norm, which is why I brought it to the Wall. Thank You all for taking interest. My service experience was more on the A/C side on computer room A/Cs and such, but had to cover anything they threw at me. Never saw this, but my leading cause is still what I laid out. You don't need a bunch of air flow, just a difference in water vapor pressure; I too, was amazed how much water had collected on the face of the burner the first time, when I took it apart. I only had to pull it out and set it on it's side to get it to drain. I will share any new findings if they show up again. And, yes, I shut the boiler off before the vacuum trick…. Did I mention that one really sharp tech that trained me early on earned the nickname "McGyver"?
    Jay W.
    Dew point in the 50s today; no worries….
    i don't know if there is a built in way to set it up as warm start at like 70 f or if you can change the setpoint for the freeze protection.
  • leonz
    leonz Posts: 1,965
    edited June 12
    The open cooled 220 volt electric motors are magnets for explosive fumes.
    You still cannot find parts to fix stupid. 😂
    109A_5 Posts: 4,617
    Too bad the Pre-Purge can't be lengthened more.
  • pedmec
    pedmec Posts: 1,488
    There is no way your getting condensation on your burner from the outside air. I've done hundreds of PM's on condensing boilers and not once have i ever i've seen any condensate formation on a burner due to dewpoints. there is all kinds of other metals in the HX that it would be getting condensation formation too.
    As others have said you either have a defective heat exchanger or a plugged drain. I would lean more toward a failed weld joint on the top plate as I have had that issue. The fire tubes are all attached to a top plate by welding. The weld will fail if the water chemical is not within tolerance. At least that's what the manufacturer will use to deny you a warranty claim. They will ask for a chemical analyst and if shows not within the allowable tolerance they will deny the claim.
    My guess is you might not see it spraying but it's happening. Just one mans opinion
    GGross
  • GGross
    GGross Posts: 2,072
    Thats a good point about the failed heat exchanger. I once pulled the top off a very leaky older triangle tube and the burner looked like a stalactite formation
  • Grallert
    Grallert Posts: 1,215
    Only $500 to fix the vacuum? I don't believe it 🤣
    PC7060