New Boiler and slight change to system installed in 2005

Options
wattz
wattz Member Posts: 1
edited 4:58PM in Radiant Heating

I have two questions about an in-floor Radiant system that was installed before I bought the place Cir 2005 or so. The home is about 4200Sq feet and was running a Buderus GB-142/45. The Boiler has been giving us problems off and on for the last 11 years. It has finally quit and I took the opportunity to try to update the system a bit.

IMG_4579.jpeg IMG_4580.jpeg IMG_4581.jpeg

as you can see the system was setup for a high temp primary loop with a injection pump to push into the secondary loop. as well as a system pump and a second system pump off the Tee to the boiler. I am trying to simplify the system and installed a hydraulic separator and just one system pump.

IMG_2030.jpeg IMG_2038.jpeg

I already know (now) that I messed up the hydraulic separator since I reused the piping the hot side is currently coming into the bottom left in the primary loop and out the top left and the same for the secondary feed side for the hot is the bottom right and return top right. I did a test run and the heat is making its way over but not as well as before with the old system. Is that mostly because I need to swap both of the in and out from the primary and secondary loops? or did I also make a mistake by taking out the pump on the primary loop. The replacement boiler is a Rinnai I-Series 150,000 BTU Combi.

Any insight would be fantastic.

Comments

  • Alan (California Radiant) Forbes
    Alan (California Radiant) Forbes Member Posts: 4,794
    edited 5:15PM

    I don’t know if it would solve your problem, but it’s important to set up counterflow in the Caleffi separator. Switch the pipes on the left side.

    And if you removed a pump on the supply side, what is left to move the water? You need something more than gravity.

    I see that you used a DWV (drainage) 90 on your piping. Not the end of the world.

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • hot_rod
    hot_rod Member Posts: 27,771

    does the boiler have a pump inside, or did it come with one?

    Pipes like this hot into top, return from bottom. On both boiler and system side

    So a boiler pump and system pump


    Is it a two temperature system still?

    IMG_2606.jpeg
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream