The Boiler Room Hero Scott Galto
In this weeks video, I do a different style of video and tell the story of Scott Galto, a stationary engineer in Dwight, IL. As he was starting the boiler, a catastrophic accident occurred
Boiler Lessons
Comments
-
Edited for typos and clarity:
Good morning and thank you Ray for the description of the actual events surrounding the steam plant accident and the heroism that Scott Galto showed that day which obviously saved many lives and prevented massive steam related damage to the steam plant at this building.
It reminds me of what happened while was sweeping the floor of the former Milliken Station power plant where I was a temp to hire employee almost 40 years ago.
Ater sweeping and mopping the floor in the control room I started sweeping the quarry tile floor of the turbine building which is the size of four football fields using an 8 foot dust mop.
When I was sweeping the floor of free of fly ash near the number two boiler there was a massive fire ball that erupted from the north wall of the dry wall boiler near where the pulverized coal was blown into the fire box of the boiler at each corner of the pulverized coal boiler.
I did not know it at the time but this was a common occurrence that happened every day.
I ran over to the nearest phone in the turbine hall and called the control room and told them about the fireball that had just occurred.
The day shift turbine operator came out and looked at where the coal fueled fire ball came out and just as he was looking at the boilers north wall one of the four coal paddle blowers blew in another batch of pulverized coal into the dry wall boiler and another huge fireball came out of the crack in the wall of the boiler.
After that he told me not to worry about it. because it was one of two dry wall pulverized combustion boilers at the power plant.
This power plant was built by Combustion Engineering at Milliken Station between 1940 and 1947 .
Go figure, I guess it was something they were going to repair after the outage started after Dave Stafford laid me off.
1 -
@leonz I would have had to change my pants seeing that. LOL I worked inside one of those coal fired power plants in Pittsburgh and it was filthy. Flyash was everywhere.
Ray Wohlfarth
Boiler Lessons0 -
Wasn't there an emergency cutoff switch at the boiler room entrance? Around here, inspectors require this…………
Baltimore, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
I don't think that I ever told my son about the dangers of operating a steam boiler. I remember a time when I didn't realize that a steam relief valve could empty the room of oxygen instantly and make that room scalding hot just as fast. When i learned about that, I always left the boiler room door open on that church steam boiler, even ig the cold days of winter.
I just texted my son who does side work on oil burners, and has one oil burner customer that has a steamer. I gave him the 2 minute course about steam displacing the oxygen and that steam is lighter than air and leave the boiler room door open. He said that i never stressed that before, I guess I just did it without telling him why, so it didn't sink in. He thanked me for the info. then went back to welding something at work.
Thanks for that story Ray. I made me make a special point about telling my son know about STEAM in a way I forgot to do, when we were working together.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
Hello Steamhead,
I am going from memory here,
No there were no exterior safety shut down controls in the power plant.
All operations of the power plant for control of the two dry wall boilers, The General Electric and Westinghouse turbines, pump floor operations the circulated 52,000 gallons per minute through the twin boilers and back to Cayuga lake after being boiled to 1,001 degrees, recirculated and scrubbed of heat twice before the water was returned to Cayuga lake at 52 degrees, the coal conveyors feeding the 4 coal bunkers, the coal feeders feeding the paddle blowers, the primary crusher under the coal stockpile, were managed in the control room. The control room had to be cooled using 100 tons of air conditioning around the clock.
The rotary coal dumper and 60 inch conveyor feeding the coal stockpile were controlled at the coal dumpers shed.
One thing that always stuck in my memory was how Mary Parkinsons young boy was injured and later died in 1977 on his birthday by being impacted by the coupler of the following empty car when he was centering the coupler to prevent the empty car from derailing.
To this day the former coal chief insists he did nothing wrong. Nothing was done to discipline the coal chief and he later bid out of the power plant job.
After the young man died they installed a safety interlock switch shed to prevent the coal chief from moving the coal cars with the radio remote control unless the laborer was standing on the switch plate.
For some backround information, the rotary coal dumper shed was installed on a curved track next to the curve of the main north south line of the railroad at the time if the coal car coupler was not returned to center the empty car would not recouple with the car ahead of it and when the locomotive pushed the next car to be unloaded through the rotary dumper the empty coal car would be derailed. The empty coal car coupler had to be centered to avoid being derailed as the loaded coal car had to be pulled back to the rotary rumper to be rolled over and unloaded.
When the power plant was built they did not need to straighten the 4 loaded car siding tracks because of the curve of the main line that was still in use. The loaded coal car tracks were set up to be operated in pairs where 2 loaded car tracks switched to the dumper track and the other loaded car tracks switched to the dumper track as well using 3 switches.
When the rotary dumper shed built was not turned to the east to straighten the exit for the 4 empty car tracks because the main line track was curved to follow the water level route to the north.
After each car was unloaded and pushed forward the empty coal car would be pushed to one of the four empty car tracks. This was managed with 3 switches for the four empty car tracks where each siding held 25 empty cars.
At the time the power plant generated 230 megawatts of power, half of which was sold and the other half delivered to the local distribution network surrounding Cayuga lake.
The power plant consumed 100 tons per hour of bituminous coal feeding the two boilers.
From what I remember of the history the powerplant was supplied with 70 ton coal cars from 1945 until they began being supplied with 100 ton coal cars that had a maximum loaded weight of 286,000 pounds.
0 -
@Steamhead Not sure they had a door switch In some large boiler rooms, I never see a door switch
@EdTheHeaterMan Youre most welcome. Im trying to pass on my knowledge before I head to the afterlife boiler room. I hope it's in the penthouse and not the basement. I always advocate opening the boiler room door until I can assure it's safe.
Ray Wohlfarth
Boiler Lessons1 -
Even in Nebraska, all boilers in commercial installations are required to have the boiler kill switch just outside the boiler room entrance.
For multiple boilers a single switch would drop out a relay for all burners.
I have had to add them on existing installations of all sizes if the installation is subject to state inspection.
0 -
@JUGHNE They are supposed to be here too but the three boiler rooms I've seen didtnt have them or I didnt see them, I thought it was due to the boiler rating. ASME CSD1 only goes ups to 12,500,000 btu I'll have to look into it
Ray Wohlfarth
Boiler Lessons0 -
Stands to reason. If something goes sideways in the boiler room you need to 1- get out of there right now, and 2- throw the emergency switch on the way out. Sometime in the last decade or so, inspectors started requiring them on at least some residential gas jobs around here, probably due to a Code change.
Baltimore, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
We were even required to add one to a Lochinvar KBN 106 in an old house used for the Parish office.
From viewing Utube channels these were common for residential oil burners.
A common call for no heat as the switch at the top of the stairs got turned off.
Now the red labeled switch plate may prevent that.
0 -
probably could do something fancy with a pilot light as a warning that the other switch was off.
0 -
Boiler room with licensed operators on duty 24/7 don't require emergency switches.
They are trained to know what to do…….supposedly.
0 -
Consider how long it takes to call the control room and tell them to perform an emergency shutdown- 60 seconds, maybe? A lot can happen in that time……………….
But it only takes 5 seconds tops to throw the emergency switch. Every boiler, of any size, should have one.
Baltimore, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
once you're dealing with a farm of powerplant size boilers shutting one or several down abruptly can have consequences that may be worse than the original incident. a trained operator needs to make the call of if and how to shut it down, a switch that anyone in the plant can push could make the situation much worse.
0 -
How so?
Baltimore, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
-
We were told that if we bumped a boiler control wall switch while sweeping the control room you can kiss your job goodbye. I was told to always tilt the dust broom handle and mop handle away from the boiler control wall.
When you were moved from the janitor job on the turbine floor you were assigned to the coal crew where you worked under the coal chief and you were given five days to learn how to work around the coal hopper cars and the locomotives. I was one that did not measure up to their standards and I was told later you should have kept your mount shut instead of telling them you were having trouble working around the coal cars.
The class one two and three railroads spend 6+ months training conductors, and track laborers to learn the jobs. dave stafford said I would never work at nyseg again. I just shook my head since some temp to hire employees never had to work on the coal crew.
0 -
Around here, on commercial jobs they want to see a lockable type of switch, basically a "one-armed" switch without fuses in it. Something like this:
https://www.supplyhouse.com/Eaton-DG322URB-Three-Phase-Non-Fusible-Disconnect-Switch-60A-240V
It would be very difficult to accidentally shut this type off by bumping it.
Even if you're using a standard wall switch with an "Emergency Switch" plate on it, you can get a guard which will prevent accidental shutoffs, like this:
https://www.supplyhouse.com/Pass-Seymour-7801P-Handle-Locking-Guard-for-Toggle-Switch
We sold a lot of these guards.
Baltimore, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1
Categories
- All Categories
- 87.7K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 127 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 121 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 79 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 17 Recall Announcements