Burnham Megasteam + HTP Superstor Ulta 60 - great combo?

Options
mcpm89
mcpm89 Member Posts: 1

Looking for ballpark pricing on Burnham oil burner MegaSteam (without coil) + HTP SuperStor Ultra 60 indirect installation in 3-family home. What's typical NYC pricing range for this scope?

Comments

  • Steamhead
    Steamhead Member Posts: 18,581

    @mcpm89 , we do NOT discuss pricing on this forum. Obviously you failed to read this:

    https://heatinghelp.com/forum-user-manual

    All Steamed Up, Inc.

    Baltimore, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,302

    @mcpm89

    If you want a good job try @JohnNY or @EzzyT . You can PM them

    mattmia2
  • pedmec
    pedmec Member Posts: 1,420

    I'm not a fan of using an indirect with a steam boiler. There is too much corrosion going on with the boiler and piping that it will cause component failures at a much higher rate than usual. You can do HX, wye strainers, etc to help protect the indirect coil but then those devices plug up and fail. I have stopped doing it that way after i had these issues pop up and it also has happened to friends of mine in the industry too. it also could be because i'm up in the northeast where steam boilers get chewed up and spit out by our water.

  • mattmia2
    mattmia2 Member Posts: 17,031

    a superstore uses a cupronickel coil.

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 12,373

    I recommend using a steam boiler with a tankless domestic hot water coil. That way, you isolate the steam boiler water from the indirect water heater loop through a heat exchanger arrangement. The wiring can remain essentially the same. You would just need to add a 30 PSI relief valve and an expansion tank on the indirect side of the system, because that portion becomes a closed-loop system heated by the tankless coil in the boiler.

    With this setup, the boiler can go cold in the summer when there is no call for domestic hot water or steam heat if you wire the system properly.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?