Energy Kinetics Gurus... Odd Energy Manager Issue
PROBLEM:
Early in a heating call, particularly when the return water temp is low, the lights on the return temp indicator will extinguish except for POWER. Sometimes 100 will flash beforehand. Sometimes it will just go blank. MONITOR light never illuminates.
The zone valve(s) close because they don't think the boiler is at 140 yet. Burner continues running as normal.
After a number of seconds have elapsed the return temp on the monitor will come back on (sometimes preceded by the 100 blinking a tad). If hot enough, zone valves open etc. Most I have seen this happen in a single heating call is twice.
PERTINENT FACTS (maybe?):
- This never happens later in a heat call
- It happens on any zone.
- 3 zones... 2 ecobees one conventional tstat
- Everything else about boiler operation is nominal
Per Energy Kinetics, if the 100 degree light blinks and MONITOR is on, the temp sensor or wiring is shot. However monitor never comes on, and their troubleshooting info does not mention anything about all the lights going on except POWER.
Any EK gurus have thoughts? @Roger
Thank you for your question, @NEMatt .The 100 degree error light will only stay lit if the sensor does not communicate properly for five minutes continuously, so the condition you’re seeing sounds like the communication is not working for periods of time that are less than that.The first things that come to mind are checking the sensor wiring (as you wiggled the wires; that’s part of the test), also check the screw tightness and then the contact from the quick connector to the circuit board edge of the manager. It could just be a sensor that needs to be replaced, or it could be aggravated by the Ecobee thermostats if they are power stealing and don’t have their own common wire. It could be an issue with the ignitor arcing to ground that is enough to interrupt the communication on the sensor, but not enough to cause further intermittent operational issues with the microprocessor on the digital manager. So the ignitor and electrodes should also be checked as it may take a little while for the sensor to recover after the ignitor turns off.
Replacing the sensor is the easiest to check, although if you don’t have one available certainly check these other things first.Best,RogerPresident
Energy Kinetics, Inc.3 -
@Roger thanks very much for the reply.
I looked at it more today and thought on it a bit more. It's almost as if the problem occurs most frequently when the return is cold and the zone valve(s) are still cycling. Once it is steadily above 130 or 140 it'll run the remaining cycle without any issues including the energy recovery period.
I also have now witnessed twice where it thought it detected a freeze condition, flashed 120, and then recovered later. This too happened early in a heat call. Makes me think the sensor is on the fritz. No reason it should read <40 degrees.
One of the Ecobees is wired with a common to the transformer, one is wired with a FastStat Common Maker as I am pretty sure this entire house was built around that original two-conductor thermostat wire! One has been wired for a couple years, the other one since December or so.
I don't think it's the ignitor since this phenomenon can happen for a few minutes depending how many zones are open and how cold the boiler/return water is. Ignitor should be off.
Probably going to replace the sensor and then see what happens.0 -
@NEMatt The system manager on your boiler uses a digital sensor. That sensor is one of the few parts unique to EK and is only available from the factory. The trade professional who services your system will be able to provide a replacement and correct this for you.Joe Szwed
Energy Kinetics0 -
That sensor is not a thermistor as it has a chip built into the probe. It cant be ordered on the internet and needs to be ordered through the factory.
John Ringel Energy Kinetics0 -
@exqheat the digital sensor (copper bulb) which is used with digital managers is not a thermistor, so the only way to test a digital sensor is by connecting to the manager itself.
@NEMatt The newer managers with the lcd display come with a dual thermistor (silver bulb) and those can be tested. At room temp (approx. 77F) it should read ~10K Ohms between the black and red wires and between the white and red wiresJoe Szwed
Energy Kinetics0 -
Yup, got it. Have one of your installers coming Friday with one.0
Have System 2000 5 zone from about 2001 with a recent problem:
When return temp is low (100deg or so), and there is a call from one of the zones via a thermostat, the system will turn on the boiler, pump and functions as normal - except acts intermittent and will suddenly shut off and turn on again right away. This occurs mainly when the water temp is low and no demand. Once the water temp is higher, above 140, this symptom is much less frequent but still may occur.
Looks to be a PCB issue, perhaps a failing relay. Problem is, there are no dealers around my area. When contacted, ALL the suggested dealers proposed by the factory do not provide service or parts for Energy Kinetics products! Any help from the factory?
thanks
@Dogsled12 , thank you for your post. I just talked with Customer Service and they indicated that you are in a remote location in Alaska. They indicated that they provided you with our territory manager in Fairbanks, AK to help diagnose and service your equipment - please reach out to him directly.
There may just be a poor wiring connection. Please see this link for a more diagnostic information. Since you are in Alaska, a service board (also shown on the link and included with your boiler) can be used to run and diagnose your equipment if there is an issue with providing heat in the interim. If the issue is with a relay for the burner/circulator, there is likely a spare/redundant relay on the relay board for an inducer (IND) that can be used (unless you have a sidewall vent).
It is also possible that the boiler side of the plate heat exchanger is substantially blocked. The burner could be turning off from the high limit control in the supply until the return hits 140°F; then the manager will open the zone valve and the system will have flow so the burner will stay running.
Thank you,
Roger
President
Energy Kinetics, Inc.1
- 87.8K THE MAIN WALL
- 129 Chimneys & Flues
- 123 Geothermal
- 79 Pipe Deterioration
- 396 Solar